#172833 - 12/27/07 09:29 PM Service Pedestal next to down spout  
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I haven't found anything in the NEC or the power company's book of codes that prevents an underground service pedestal being installed next (12"-16")to a downspout. Has anyone failed an inspection for this? Note: the downspout discharges into a drain tile.


Jesus may have been a capenter,but God was an electrician.Genesis1:3

Work Gear for Electricians and the Trades

#172866 - 12/28/07 01:33 PM Re: Service Pedestal next to down spout [Re: bot540]  
JValdes  Offline
Member
Joined: Jun 2007
Posts: 301
South Carolina
Your okay. Conductors must be suitable for direct burial or if in conduit the conductors must be rated for wet locations. Like THHW.



Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.003s) Memory: 0.7431 MB (Peak: 0.8587 MB) Zlib enabled. Server Time: 2017-09-23 18:12:34 UTC