#17260 - 11/22/02 06:11 PM 15kV Underground - Spare Conduits  
WJH  Offline
Junior Member
Joined: Nov 2002
Posts: 1
Shawnee, KS, United States of ...
We are working on a meat packing plant that will have a 15kV lineup of outdoor metal-enclosed load interrupter switchgear. These switches will feed pad mount transformers (underground concrete encased PVC ductbank) which will serve 480/277V main-tie-main switchboards located throughout the facility. Should we provide a spare conduit for each 15 kV feeder? Pros? Cons?


Work Gear for Electricians and the Trades

#17261 - 11/22/02 08:18 PM Re: 15kV Underground - Spare Conduits  
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
I wouldn't provide one if it is not provided for in your contract. It's funny that you should ask because every medium voltage ductbank that I've ever been involved in had a spare conduit in it. That especially holds true for primary coming from the utility.
Hit the customer up for an extra. If they ever have a failure without an extra conduit to pull in a new feeder, they may regret having not provided one while the project is under construction.

Extra Change, Bling, bling,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX

#17262 - 11/24/02 10:37 AM Re: 15kV Underground - Spare Conduits  
fedup  Offline
Member
Joined: Oct 2001
Posts: 31
alabama
the major cost in installing your ductbank is in the excavation and placement of concrete.An extra 5" conduit won't add to much to the cost.If the runs are long I would intall steel 90's have seen the pull rope burn through pvc more times than I would care to say



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.7513 MB (Peak: 0.8752 MB) Zlib enabled. Server Time: 2017-05-26 22:37:05 UTC