#171968 - 12/09/07 07:55 PM Question On Floor Mounted Receptacles In Dwelling?  
HERMIT  Offline
New Member
Joined: Dec 2007
Posts: 1
Ontario
Hello--I am new to the forum and have a question.
I was in a discussion on installing floor mounted receptacles in a home. I have never run across this myself but thought it was against code in Ontario.
Does anyone know for sure and where I'd come across the rule in a Codebook? Thanks.
Here is a link showing a box in question:
http://www.hometech.com/techwire/floorbox.html


Tools for Electricians:

#171973 - 12/09/07 08:25 PM Re: Question On Floor Mounted Receptacles In Dwelling? [Re: HERMIT]  
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
Hermit,

First welcome to the forum. I cant tell you where to find it in your code( i am from US), but I can tell you that there was a recall on those floor boxes in the US because the hot and neutural wires were put on the wrong side of the receptacle. Be sure to check polarity before, if, you install any of them


Jimmy

Life is tough, Life is tougher when you are stupid

#171985 - 12/10/07 09:08 AM Re: Question On Floor Mounted Receptacles In Dwelling? [Re: wire_twister]  
Rick Kelly  Offline
Member
Joined: Jan 2006
Posts: 60
Iqaluit, NU, Canada
While not sure about the Ontario Code, the CEC allows them as long as they are installed in an approved box designed to protect the receptacle from water and dust penetration.

The CEC rule is 26-700(5).

Rick...


#172000 - 12/10/07 06:15 PM Re: Question On Floor Mounted Receptacles In Dwelling? [Re: HERMIT]  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Here in Ontario, we install dozens of floor plugs in the custom homes we do. We use the Pass and Seymour kits. Click on their website and type "floor box" on their search engine.


#172035 - 12/11/07 12:37 PM Re: Question On Floor Mounted Receptacles In Dwelling? [Re: Sandro]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
See 26-700(5) It states that boxes in floors must be floor boxes.



Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.004s) Memory: 0.7678 MB (Peak: 0.9112 MB) Zlib enabled. Server Time: 2017-11-19 14:13:40 UTC