#171919 - 12/08/07 08:42 PM Shunt Trip Breaker Wiring  
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I need to install a few shunt trip Square D QOB breakers and was wondering how exactly are these things are wired. Off the ansul system I have three wires yellow, brown, and blue. I believe that the yellow is the common and the blue is the normally closed contact, which make the brown the normally open contact.
I am assuming you hook the breaker up to the normally open contact. Is this correct?


Jesus may have been a capenter,but God was an electrician.Genesis1:3

Work Gear for Electricians and the Trades

#171927 - 12/08/07 10:36 PM Re: Shunt Trip Breaker Wiring [Re: bot540]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Yellow should be common,brown N/O.
Dedicate a ckt from a NON-shunted panel to this contact. then to the ST brkr/brkrs.On activation the relay closes and shunts the brkr. Panel down.
The exhaust fan/s should not be shunted on deployment.


#171931 - 12/08/07 10:59 PM Re: Shunt Trip Breaker Wiring [Re: leland]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
====The exhaust fan/s should not be shunted on deployment. ==

I'll retract this, untill I can quote the art.
It is common practice, I just can't find it rght now.


#171933 - 12/08/07 11:24 PM Re: Shunt Trip Breaker Wiring [Re: leland]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA

NFPA-17A-
4.4.3.5-- Exhaust fans do not need to be shut down on deployment of the wet system.


But in 5.6.2.2- all fuel and heat sources MUST be shut down.
easy to shunt trip the panel.
4.4.3.4- solid fuel- needs no shut down.Fancy Pizza joint--(Joint mmmm)
4.4.3.7- requires all shut down devices need a manual reset.
shunt trip brkr, coverd.


#171940 - 12/09/07 06:47 AM Re: Shunt Trip Breaker Wiring [Re: bot540]  
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
So the breaker needs a 120 volt signal to trip?


Jesus may have been a capenter,but God was an electrician.Genesis1:3

#171941 - 12/09/07 07:51 AM Re: Shunt Trip Breaker Wiring [Re: bot540]  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
The shunt trips I've wired need 120v signal to trip


#171944 - 12/09/07 08:26 AM Re: Shunt Trip Breaker Wiring [Re: walrus]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
I much prefer using a contactor instead of shunt trip breakers.
They don't take up valuable space in the panel (shunt trips take an extra pole space for the trip), and are more economical.


#171945 - 12/09/07 09:12 AM Re: Shunt Trip Breaker Wiring [Re: electure]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Agree, if you only have a few peices of equipment to shut down, contactor may be more economic.
Most gas equip. will have a mechanicle gas valve shut off.

Only the equipment in the protected area (hazard) needs to be dumped. Check your local codes and follow specs.

Last edited by leland; 12/09/07 09:13 AM.

#171947 - 12/09/07 10:00 AM Re: Shunt Trip Breaker Wiring [Re: walrus]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by walrus
The shunt trips I've wired need 120v signal to trip
I've seen some with 24VDC and 48VDC shunt trip- you'd need to check the specs on the breaker as to what it needs.

Should be OK to feed shunt-trip from this panel. After all, it will have power TO shunt trip, and after shunt trip... you don't really need power anymore!

Also, you might want to note somewhere on the panel that it's configured to shunt trip. We had one go off once over lunch when a contractor working sprinklers in another part of the building opened a valve just outside a data center to bleed the system and a flow sensor shunt-tripped the main breaker and killed power to the data center. DOH! None of the ITs had any clue what had happened or how to recover, and were running around trying to figure out why the generator hadn't started. - NOTHING was labeled, neither the panel nor the sprinkler. It's labeled now.

Last edited by SteveFehr; 12/09/07 10:06 AM.

#171948 - 12/09/07 10:43 AM Re: Shunt Trip Breaker Wiring [Re: SteveFehr]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
I've done that! Wow,they don't like it much.
Coz everybody looses 10, mil$ a minute. Just ask them.


Page 1 of 2 1 2

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,262
Joined: December 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 16 (0.003s) Memory: 0.8176 MB (Peak: 0.9993 MB) Zlib enabled. Server Time: 2017-11-24 03:31:28 UTC