#170486 - 11/04/07 11:14 AM wire size  
drkana  Offline
New Member
Joined: Nov 2007
Posts: 4
illinois usa
what size wire in paralell is equal to 300 mcm and is there a reference table somwhere?


Tools for Electricians:

#170491 - 11/04/07 12:57 PM Re: wire size [Re: drkana]  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
See Table 8 in Chapter 9

Roger


#170515 - 11/04/07 10:29 PM Re: wire size [Re: drkana]  
drkana  Offline
New Member
Joined: Nov 2007
Posts: 4
illinois usa
looking at that table it looks like 3/0 or 2/0 but i'm not sure any suggestions.


#170564 - 11/05/07 10:22 PM Re: wire size [Re: drkana]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
What are you trying to do?
Don


Don(resqcapt19)

#170567 - 11/06/07 07:22 AM Re: wire size [Re: resqcapt19]  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
2/0 won't make it but, I think Don's question needs to be answered, it may save you some grief.

Roger


#170615 - 11/07/07 08:30 AM Re: wire size [Re: Roger]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
With alternating current, magnetic fields build up inside the cable and skin resistance comes into play, so cable ampacity doesn't scale linearly with cross-section. In addition, cooling is related to the surface area of the cable, and larger cables have less surface area than two smaller ones to dissipate heat. Ergo, you can safely (and legally) carry more current through 2x 150MCM than through 1x 300MCM, and 2x 1/0 may be sufficient depending on what you intend.

If you're talking DC, reference Chapter 9, Table 8. If you're talking 60Hz AC, reference a combination of 310.60 with the derating rules of 310.1(B)(2)(a)... and the myraid of other codes that may apply.

Last edited by SteveFehr; 11/07/07 08:33 AM.

#171088 - 11/19/07 03:50 PM Re: wire size [Re: SteveFehr]  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Table 310.16 takes all of this into consideration. Assuming THWN insulated copper conductors, 300 kcmil has an ampacity of 285 amps, therefore 2 paralleled 1/0 AWG conductors in separate conduit or cable would have equivalent current carrying capacity. It is necessary to keep these paralleled conductors in separate conduit or cables because of the heat buildup when more than 3 current carrying conductors are installed in one conduit (300.15(B)(2)(a))


Earl


Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7831 MB (Peak: 0.9409 MB) Zlib enabled. Server Time: 2017-10-17 01:58:01 UTC