210.52 Clear as Mud #170447
11/03/07 08:06 AM
11/03/07 08:06 AM
R
rowd  Offline OP
Member
Joined: Sep 2002
Posts: 31
Park Forest, Illinois, USA
In the illustration linked from the NEC it shows 4 feet between receptacles.The code states "Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space."

Clear as mud. once again the NEC manages to make a ruling even more muddled than it ever was to begin with.


(1) Wall Counter-top Spaces. A receptacle outlet shall be installed at each wall counter-top space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space. See related Illustration

Exception: Receptacle outlets shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink in the installation described in Figure 210.52(C)(1).

[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: 210.52 Clear as Mud [Re: rowd] #170449
11/03/07 08:28 AM
11/03/07 08:28 AM
R
rowd  Offline OP
Member
Joined: Sep 2002
Posts: 31
Park Forest, Illinois, USA
Sorry.....Here is the illustration

[Linked Image]

Re: 210.52 Clear as Mud [Re: rowd] #170450
11/03/07 08:55 AM
11/03/07 08:55 AM
J
JohnJ0906  Offline
Member
Joined: Oct 2006
Posts: 65
Baltimore MD USA
Exactly what is unclear?

Re: 210.52 Clear as Mud [Re: JohnJ0906] #170452
11/03/07 09:47 AM
11/03/07 09:47 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Seems pretty clear to me ... unless you are not sure how these things are measured.

Receptacle spacing is determined by measuring, as it were, along the baseboard (or, with counters, the backsplash). There is no allowance for the height a receptacle may be above the floor (or counter). Things that interrupt the 'usable' path (doors, sinks, ranges) are not included in the measure. If the path takes a turn, the measure follows the turn - as shown in that corner.

Legal line aside .... go buy a cheap toaster. If the cord can't reach a receptacle, you probably need to add one at that point.

Re: 210.52 Clear as Mud [Re: renosteinke] #170481
11/04/07 08:48 AM
11/04/07 08:48 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 927
Chicago Illinois USA
I always figured that it was to make sure that there was always a receptacle within 2' of any point along the wall to go along with the standard length of appliance cords.

The 12" countertop rule probably arose because folks started putting a short piece of countertop between the stove and the end wall...and some genius ran an extention cord to it for the toaster.


Ghost307
Re: 210.52 Clear as Mud [Re: ghost307] #170495
11/04/07 02:41 PM
11/04/07 02:41 PM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
The key word is point. No point shall be more than 2 feet.
This same confusion occurs when receptacles in habitable rooms are to be no more than six feet from a point. The receptacles are twelve feet apart.


Alan--
If it was easy, anyone could do it.
Re: 210.52 Clear as Mud [Re: Alan Nadon] #170514
11/04/07 08:50 PM
11/04/07 08:50 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.


Greg Fretwell
Re: 210.52 Clear as Mud [Re: gfretwell] #170557
11/05/07 07:58 PM
11/05/07 07:58 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
I have heard of some that did not interpret this measurement as being along the back part of the countertop and actually wanted a receptacle mounted on the 24" depth of the side wall where the countertop meet the wall.

Re: 210.52 Clear as Mud [Re: Jim M] #170559
11/05/07 08:28 PM
11/05/07 08:28 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
You just defined the argument. It doesn't say "back" wall. wink


Greg Fretwell
Re: 210.52 Clear as Mud [Re: gfretwell] #171777
12/05/07 12:45 PM
12/05/07 12:45 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by gfretwell
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.
I think it should be changed, though, to "any point on the counter" within 2', though. What good is a rule to allow 2' cords to be used anywhere if they still can only be used butted up against the wall?

I know, I know, counters are 2' deep, and we'd need a continuous outlet for this. Really, it begs the question ... why the $&#&#$^%$^ are they only 2' cords to begin with? Why can't I get a blender with a 4' cord and a lamp with a 12' cord? Why always the rinky short cord?

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,596 Are you busy
180,399 Re: Forum
170,866 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 16 (0.004s) Memory: 1.0250 MB (Peak: 1.2052 MB) Zlib enabled. Server Time: 2018-01-23 04:07:53 UTC