ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
75 kva tranformer
by sparkync. 09/23/17 06:41 PM
Another generator question
by gfretwell. 09/23/17 04:15 PM
What do you do?
by gfretwell. 09/22/17 10:37 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,905 Are you busy
176,671 Re: Forum
168,562 Need opinion
Who's Online Now
0 registered members (), 36 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#170261 - 10/30/07 02:57 PM Panel enclosure as raceway  
bman  Offline
Member
Joined: Jul 2006
Posts: 20
or
Have a job that requires "swapping" of circuits from one panel to another. Past experience tells me that one must remove said circuits entirely from panel enclosure as it is not permissible to use a panel or disconnect enclosure as a raceway for other systems. I got to looking at 300.3 4C and 312.8 and it would seem to cover panel board enclosures so long as sufficient space exists for wire fill. Thoughts?


2017 / 2014 NEC & Related Books and Study Guides

#170371 - 11/01/07 08:05 PM Re: Panel enclosure as raceway [Re: bman]  
bman  Offline
Member
Joined: Jul 2006
Posts: 20
or
Guess its a good thing this didn’t come up on anyone’s Journeyman’s test.


#170427 - 11/02/07 08:12 PM Re: Panel enclosure as raceway [Re: bman]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 826
Michigan
408.2 says 312 applys so I;d say yer right . Long as space is there.


#170456 - 11/03/07 12:26 PM Re: Panel enclosure as raceway [Re: Yoopersup]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,117
Estero,Fl,usa
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".


Greg Fretwell

#170546 - 11/05/07 05:11 PM Re: Panel enclosure as raceway [Re: gfretwell]  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Originally Posted by gfretwell
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".


You can't just take the first part of a sentence and ignore the rest.

You are allowed to use a panel as a jbox provided you meet the rest of 312.8 and unless you are really loading up the panel with splices or it is an older smaller panel there should be plenty of room.


#170561 - 11/05/07 09:50 PM Re: Panel enclosure as raceway [Re: Electricmanscott]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,117
Estero,Fl,usa
Scott, If I was looking at this and it was done in such a way that did not clutter up the panel too bad I wouldn't have a problem with it but I know some guys who dissagree and have a very limited interpretation of what 312.8 allows.
I have even heard more restrictive spins on this in IAEI seminars from respected road warriors.


Greg Fretwell


Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.7768 MB (Peak: 0.9270 MB) Zlib enabled. Server Time: 2017-09-24 08:38:40 UTC