ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
jraef 4
Recent Posts
Dryer, Range grounding from "Main" panel
by gfretwell. 05/24/17 12:56 AM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
Interesting week
by HotLine1. 05/20/17 11:57 AM
Electrical Pricing Guide
by ElectricianBud. 05/18/17 12:17 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,705 Are you busy
171,709 Re: Forum
164,659 Need opinion
Who's Online Now
0 registered members (), 64 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#169841 - 10/17/07 09:17 PM Gfi's and testers.  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Could use some insight on this; gfi receptacle trips with 'test' button, but not with a gfi tester. New type that supposedly won't work if wired wrong. Tester is ok. Ideas ?


Work Gear for Electricians and the Trades

#169843 - 10/17/07 09:29 PM Re: Gfi's and testers. [Re: derater]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,077
Estero,Fl,usa
No ground?


Greg Fretwell

#169846 - 10/17/07 10:32 PM Re: Gfi's and testers. [Re: gfretwell]  
SP4RX  Offline
Member
Joined: Oct 2007
Posts: 56
Edmonton, Alberta, Canada...eh
I agree with Fretwell. I think that the gfi tester works by allowing a small amount of current to flow from the hot conductor through a resistor to the grounding conductor. So if you have no ground connection at the gfi the tester's ground prong wouldn't have a good return path for the simulated ground fault.
This doesn't mean that the gfi won't work as intended though since it normally compares line current to neutral current, with no need for a ground.
Perhaps you could verify it's correct operation by unscrewing the gfi and, using a separate wire, make a temporary connection to a good remote ground point and then try your tester again?

Shawn.


#169858 - 10/18/07 12:54 PM Re: Gfi's and testers. [Re: SP4RX]  
JValdes  Offline
Member
Joined: Jun 2007
Posts: 301
South Carolina
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.


#169859 - 10/18/07 01:12 PM Re: Gfi's and testers. [Re: JValdes]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,205
Chesapeake, VA
Originally Posted by JValdes
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.
The GFCI will still work properly without a ground (hence its acceptability in ungrounded retrofit appliations) but the GFCI tester wouldn't work, as it can't shunt a small amount of current to ground if there's no ground to shunt to. Standing in a puddle and sticking a wet finger into the receptacle aught to do the trick, though. But it's certainly not recommend as the consequences if the test fails are potentially rather dire...

Last edited by SteveFehr; 10/18/07 01:13 PM.

#169865 - 10/18/07 03:56 PM Re: Gfi's and testers. [Re: SteveFehr]  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Thanks all. That's the case, no ground.



Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.7760 MB (Peak: 0.9215 MB) Zlib enabled. Server Time: 2017-05-24 15:36:35 UTC