#169317 - 10/01/07 06:25 PM 480v parking lot lighting  
etech  Offline
Member
Joined: Jun 2007
Posts: 17
Oregon
We reto-fitted parking lot lighting from 208v to 480v, one ckt. keeps shorting out. Wire is rated for 600v. Lights work for two months at a time. Any feed back will be welcomed.


Work Gear for Electricians and the Trades

#169318 - 10/01/07 06:55 PM Re: 480v parking lot lighting [Re: etech]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
what the oringail luminaire wired on 120 v or 208 volt??

and i will suggest to megger the line to find out sometime you will get a bad spot of wire.

rule of thumb anytime you increase the voltage on parking lot luminaire system is megger it first if the wire are fine otherwise replace it.

that useally take care of bad curpits with connection and who know what happend in the pipe as well

what the wattage on the luminaires now ?? and the voltage it is on now 277 or 480 ??

if the megger pass the test then you should amprobe it to check the current drawage make sure it dont get too much loading escpally with the MWBC set up

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#169322 - 10/01/07 09:49 PM Re: 480v parking lot lighting [Re: frenchelectrican]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Such problems can be quite vexing.

What I ended up doing in a similar situation was to put in-line fuses on BOTH wires, at the base of the fixture. I was then able to identify the fixtures that were giving us trouble.


#169330 - 10/01/07 11:56 PM Re: 480v parking lot lighting [Re: renosteinke]  
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 854
Titirangi, Akld, New Zealand
As already said by frenchelectrician, sectionalise and megger all cables concerned and check the insulation resistance between cables to lamps.
Hopefully you don't have breach joints in the SL circuits.
These usually get damp because of poor sealing of the outer sleeving.
The increased voltage will cause them to break down faster and hence intermittand faults once in a while.

From control point lightcell contactor, fit section fuses on each outgoing SL circuit.

Also check the overall loading per string of lights.

Fit fuses in each lamp acces cover if not already there.


The product of rotation, excitation and flux produces electricty.

#169352 - 10/02/07 07:50 PM Re: 480v parking lot lighting [Re: RODALCO]  
sparkyinak  Online Content
Member
Joined: Jul 2007
Posts: 1,322
Alaska
I would account for all the runs of wires in case the origional circuit picked up an remote outlet or some other light like a lighted sign or something. Being that the voltage was boosted, if anything was left on circuit, it is safe to say it's toast. Eliminate the easy things first before megging the wires or adding fuses. Do you recall the weather conditions a few days before the outage(s)?


"Live Awesome!" - Kevin Carosa


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.7692 MB (Peak: 0.9122 MB) Zlib enabled. Server Time: 2017-05-28 22:12:11 UTC