#167855 - 08/21/07 07:17 PM Sub-Panel Grounding and BX/AC 250.32(B)  
JJM  Offline
Member
Joined: Oct 2005
Posts: 100
I've been having a bit of debate with a colleague on sub-panel grounding on buildings wired with BX/AC as it relates to NEC 250.32(B)

Typically, sub-panels are wired with a separate ground and floating neutral, but what about with systems wired with BX/AC? Can that fourth wire be eliminated in this case, since the grounding equipment conductor is the cable sheathing or conduit? Can the cable sheathing or conduit technically be classified as a "conductor" from a code standpoint?

The reason I'm asking is we got a request to add a sub-panel in a small warehouse (for 240V loads) in NYC, previously powered by only a single 20A breaker. The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.

My colleague says all he does is simply adds a grounding bushing at the sub, and runs the ground from the bushing to the grounding bus... and has never been tagged, nor should he be. He argues there is absolutely no reason to run a separate ground, since the wiring system designates the cable sheathing (or conduit) as the ground - unless the conduit is in bad shape in which case it should be dug up anyway.

He further argues since this is not a new service, inspectors won't require a ground to be pulled, as we would be required with new services... and not "open their eyes" on this... unless I want to break out the jackhammer. Needless to say, there will be quite a difference quoting this job with and without breaking up concrete.

What say all of you on this one?

Joe


Work Gear for Electricians and the Trades

#167875 - 08/21/07 10:44 PM Re: Sub-Panel Grounding and BX/AC 250.32(B) [Re: JJM]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
If this is really "rigid" (RMC) in good shape and you put bonding bushings on each end I have no problem with this being the EGC. That actually exceeds code.


Greg Fretwell

#167876 - 08/21/07 11:08 PM Re: Sub-Panel Grounding and BX/AC 250.32(B) [Re: gfretwell]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
-The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.-


Is the rigid run from panel to panel? If so good.

Or are you pulling an AC feeder thru it as a chase


#167910 - 08/22/07 07:02 PM Re: Sub-Panel Grounding and BX/AC 250.32(B) [Re: JJM]  
JJM  Offline
Member
Joined: Oct 2005
Posts: 100
Thanks for setting the record straight. I owe my colleague an apology.

I guess I was too rigid (no pun intended) in interpreting the term conductor in 250.32(B), and am sure glad we won't need to break out the jackhammers on this one. Doesn't matter if you're getting paid or not, it's never fun.

The rigid is in good shape, installed about a decade ago. The galvanized doesn't run straight to the panel - runs up to an LB, then nipplies into a J-box - so we'll just upsize the BX to the J-box and bush it... exactly as my "old timer" colleague originally suggested.

Thanks again for the always best advice.

Joe



Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7616 MB (Peak: 0.8947 MB) Zlib enabled. Server Time: 2017-05-29 15:10:31 UTC