ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 3
Recent Posts
FPE in Germany
by Texas_Ranger. 11/19/17 07:30 AM
Ceiling fan distance from outdoor hot tub
by gfretwell. 11/16/17 02:18 AM
diazed fuses
by Texas_Ranger. 11/13/17 03:02 PM
Theft deterrent alarm
by gfretwell. 11/12/17 01:39 PM
EEPROM errors on XC7Z010-2CLG225I chip
by twh. 11/07/17 05:45 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,603 Are you busy
178,785 Re: Forum
170,039 Need opinion
Who's Online Now
0 registered members (), 28 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#167751 - 08/19/07 02:26 PM Circuit Design  
windmiller  Offline
Junior Member
Joined: Dec 2006
Posts: 43
Alaska
Whats the rule on feeding a 300A Fused Disconect from a 400A breaker?

thanks

Windmiller


We all live under one King

2017 / 2014 NEC & Related Books and Study Guides

#167759 - 08/19/07 07:05 PM Re: Circuit Design [Re: windmiller]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
More info required for answer.


John

#167768 - 08/19/07 09:39 PM Re: Circuit Design [Re: HotLine1]  
windmiller  Offline
Junior Member
Joined: Dec 2006
Posts: 43
Alaska
Hi,
This is from a 480 V MCC to a maint. shop.

This is a feeder to supply power to the building.

No 300A plug in bucket is available and no other place to get power except from 480V MCC with a new section and a frame mounted 400 CB.

The feeder is 3/C 500 MC.

Thanks,

Windmiller


We all live under one King

#167770 - 08/19/07 09:56 PM Re: Circuit Design [Re: windmiller]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
500 MCM is 380a @ 75c
I don't see a real problem. If you can get in under the feeder tap rules it is a slam dunk and you can probably use 240.4(B) if it comes down to it.

From a practical sense, you are really only providing short circuit protection in the 400a breaker since overload protection will come with the 300a. That is how they rationalize the "tap rules".

Last edited by gfretwell; 08/19/07 09:57 PM.

Greg Fretwell

#167907 - 08/22/07 01:36 PM Re: Circuit Design [Re: windmiller]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
Quote
This is a feeder to supply power to the building.


If so, it may qualify for an outside the building tap of unlimited length per 240.21(B)(5)



Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.7683 MB (Peak: 0.9081 MB) Zlib enabled. Server Time: 2017-11-21 15:23:12 UTC