#165690 - 07/03/07 11:57 AM transformer grounding  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
a 480-120/240 50kva dry transformer, i am doing the bonding in the trans. do i ground the trans. frame with the 480 ground and remove the 120/240 strap to the frame. all raceways are pvc with on the 480 side i have 2 phases and a ground. also this trans is mounted on a portable plant with the 120/240 volt panel, the trans and panel are on the same steel frame. what is the proper grounding and bonding.


2017 / 2014 NEC & Related Books and Study Guides

#165701 - 07/03/07 03:36 PM Re: transformer grounding [Re: lite bulb]  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Leave the strap to the frame in place.

Bond the green wire from the 480 volt side and the green wire on the 120/240 side and the building steel and any metal water pipes in the vicinity served by the secondary to the enclosure. the strap will connect the equipment grounding system to the neutral connection of the transformer.

The objective here is to clear any ground faults by ensuring a low impedance path back through the equipment ground to the neutral connection at the transformer.

On the 480 volt side, the equipment grounding conductor needs to also be connected to the enclosure to create a low impedance path back to the 480 volt distribution center, then to the service and back to the utility transformer to clear any faults to the transformer enclosure.

We cannot clear any ground faults without a complete low impedance path through the equipment grounding system.


Earl

#165713 - 07/03/07 08:13 PM Re: transformer grounding [Re: earlydean]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
thanks for the help


#165714 - 07/03/07 11:02 PM Re: transformer grounding [Re: lite bulb]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Make sure that the neutral on the secondary side is bonded to a grounding electrode system and to the EGCs for the loads. Many of the bonding straps in the transformer only bond the frame of the transformer to the case. Sometimes they bond the secondary neutral, but that is somewhat rare nowdays.
Don


Don(resqcapt19)


Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7600 MB (Peak: 0.8951 MB) Zlib enabled. Server Time: 2017-05-01 06:23:20 UTC