90 Degree EMT Wire Pull Connector In Wall? #165567
06/30/07 01:43 PM
06/30/07 01:43 PM
I
InspectorE  Offline OP
Member
Joined: Oct 2004
Posts: 51
Hudson WI USA
Is it code compliant to use a 90 degree EMT wire pull as a sharp right angle turn through a wall? The construction is structural insulated panel with 2x2 furring strips. There isn't enough room to simply use a conduit bender, but a sharp 90 degree would work. The 90 degree wire pull EMT connector will work physically, but can it be used in this application? The wire pull is NOT needed due to the 360 degree total turn limit.

The wire pull is certainly rated for use where it is accessible; the question is can it be used where it is not necessary to be accessible? This is kind of like a doctor prescribing a drug for "off label use". If not acceptable, can you quote a NEC section?

Thanks guys

Frank

2017 / 2014 NEC & Related Books and Study Guides
Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: InspectorE] #165568
06/30/07 02:15 PM
06/30/07 02:15 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
300.15(A) "...The covers shall be accessible after installation"
300.18 Raceway Installations.
(A) Complete Runs. Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors.


Greg Fretwell
Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: InspectorE] #165685
07/03/07 07:56 AM
07/03/07 07:56 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Originally Posted by InspectorE
"90 degree EMT wire pull"


Do you mean an LB, LL, LR, or "Pulling Ell"? If so, the answer is no.

I ask because there are still some short radius benders out there that still fit the bill for the listed radidus in the code.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: e57] #165686
07/03/07 09:16 AM
07/03/07 09:16 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
He might mean a 90 flex connector ... which I have seen used on EMT frown

The short answer ... if you can't pull wires through it, you can't bury it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,231
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,543 Are you busy
180,346 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 0.9595 MB (Peak: 1.0915 MB) Zlib enabled. Server Time: 2018-01-19 03:47:06 UTC