ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by ElectricianBud. 05/27/17 11:02 AM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,930 Are you busy
171,941 Re: Forum
164,827 Need opinion
Who's Online Now
0 registered members (), 53 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#16376 - 11/10/02 10:13 PM Derating  
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
I noticed in a foundry that their electric conduits in the ceiling to feed various equipment looked like spegheti. The company would like to run major conduit runs through 2 or 3 large J.B.a spread out all overhead around different areas where you can just pipe up and attach electric equipment hard wired, spliced, and ran through a larger conduit back to the panelboard. There could be a possbility of 10-20 ckts. Does the derating factors of 310-16 apply here, and if so, does this installation warrant???

[This message has been edited by Wirenuttt (edited 11-10-2002).]


Work Gear for Electricians and the Trades

#16377 - 11/11/02 07:25 AM Re: Derating  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
welcome Wirenuttt
[Linked Image]

IMO, derating would apply, T310.15(B)(2)(a) would dictate 50% off of 310.16 ( 10-20 conductors), however note the math starts at the 90degC collum there.

some consideration for the cieling 'ambient' temp may also apply

The interesting thing is the JB vs. a trough, and the magic '29' conductor limit here;

Quote
376.22 Number of Conductors.
The sum of the cross-sectional areas of all contained conductors at any cross section of a wireway shall not exceed 20 percent of the interior cross-sectional area of the wireway. The derating factors in 310.15(B)(2)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions of 310.15(B)(4), exceeds 30. Conductors for signaling circuits or controller conductors between a motor and its starter and used only for starting duty shall not be considered as current-carrying conductors.

[Linked Image]



Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7440 MB (Peak: 0.8614 MB) Zlib enabled. Server Time: 2017-05-28 14:25:33 UTC