ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
VDE 0100 to introduce AFCIs
by sparky. 01/19/18 08:03 PM
MRI LED lights dimmer control replacement - wow!
by HotLine1. 01/19/18 06:19 PM
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
1 registered members (sparky), 19 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Single Phase 220V from 3 phase Y 208 #162912
04/27/07 04:13 PM
04/27/07 04:13 PM
G
GCI  Offline OP
New Member
Joined: Apr 2007
Posts: 1
AZ, USA
I have 3 phase Y 208 at my office. Purchased a lift that has a pump motor on it that requires 220 sigle phase. Any two legs of three phase are 120 degrees out of phase, I have seen wiring for welders wired this way, but a - motor probably requires 180 degrees phase difference? Step up transformer or other solution?

Work Gear for Electricians and the Trades
Re: Single Phase 220V from 3 phase Y 208 [Re: GCI] #162921
04/27/07 05:51 PM
04/27/07 05:51 PM
R
RobbieD  Offline
Member
Joined: Feb 2003
Posts: 231
Canada
Just hook it up to 208V. It will work fine.

What type of engineer are you?

Re: Single Phase 220V from 3 phase Y 208 [Re: GCI] #162937
04/27/07 07:13 PM
04/27/07 07:13 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by GCI
I have 3 phase Y 208 at my office. Purchased a lift that has a pump motor on it that requires 220 sigle phase. Any two legs of three phase are 120 degrees out of phase, I have seen wiring for welders wired this way, but a - motor probably requires 180 degrees phase difference? Step up transformer or other solution?


2-wire motors are wired line-line. There is no phase difference between only two wires. The concern is that you actually have enough voltage to run your motor, the worst case is you will need to use a buck-boost transformer. Is your motor really 220V and not 230V?

Re: Single Phase 220V from 3 phase Y 208 [Re: JBD] #163009
04/28/07 10:01 PM
04/28/07 10:01 PM
D
Dave T  Offline
Member
Joined: Jan 2005
Posts: 155
Waukesha, WI, USA
Have you asked the manufacturer or the pump motor manufacturer??
This is not to be taken for an answer to you application but some background for the answer you should get from the manufacture.
If in fact it is a 220v motor od it NEMA rated? If so antivipate that it is able to operate satisfactory a +-10% of that which would be 220 x.90=198v. I did not say that the device was capable to operate at down to 198v but there's a good chance that it would be an accurate answer.
Remember one thing. If a motor is rated at 10HP at 220v it will draw a specific amount of amps to product 10HP. In doing so there will be losses in heat. Now reduce that voltage to 198v. To produce the same 10HP the motor would have to draw more amps to produce that same 10HP. More amps = more heating.
It is common that whem a motor is applied it never is required to produce its nameplate HP anyway.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 15 (0.004s) Memory: 0.9586 MB (Peak: 1.0911 MB) Zlib enabled. Server Time: 2018-01-20 01:08:16 UTC