running cat5e #159799
01/30/05 05:00 PM
01/30/05 05:00 PM
D
dryden_burton  Offline OP
Member
Joined: Nov 2004
Posts: 11
Maple Creek, Saskatchewan, Can...
is running cat5e in heating ducts alowed ?


Dryden
Study Guides for VDV / Structured Cabling Installers

Voice, Data, Video, (VDV) Fiber Optics, Communications, Low Voltage,
Fire Alarm, Electronic Security Systems Installations & Related

NTC Low Voltage Training & NICET Exam Study Guides
Low Voltage Training & NICET Exam Study Guides

Re: running cat5e #159800
01/30/05 05:12 PM
01/30/05 05:12 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Simple answer: No
Little more specific: you can go THROUGH, at ninety degrees. I would infer that cable should then be plenum rated.

Re: running cat5e #159801
01/30/05 06:28 PM
01/30/05 06:28 PM
D
dryden_burton  Offline OP
Member
Joined: Nov 2004
Posts: 11
Maple Creek, Saskatchewan, Can...
i didnt think so
ok thanks


Dryden
Re: running cat5e #159802
02/01/05 04:18 PM
02/01/05 04:18 PM
D
dstanford  Offline
Member
Joined: Dec 2004
Posts: 23
Asheville NC USA
i don't think you can run through ducts even at 90 degrees... where did you see that at renosteinke. why that would be something to take a picture of and submit to the picture forum

Re: running cat5e #159803
02/01/05 07:47 PM
02/01/05 07:47 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Not that its a great practice, it is allowed with some limitation. (With Plenum rated cable...)

Quote
800.53 (A)Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CMP. Abandoned cables shall not be permitted to remain. Types CMP, CMR, CMG, CM, and CMX and communications wire installed in compliance with 300.22 shall be permitted. Listed plenum communications raceways shall be permitted to be installed in ducts and plenums as described in 300.22(B) and in other spaces used for environmental air as described in 300.22(C). Only Type CMP cable shall be permitted to be installed in these raceways.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: running cat5e #159804
02/01/05 08:15 PM
02/01/05 08:15 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Looks like I get smacked for "shooting from the lip." Apparently I was repeating something I'd heard, rather than actual code. Of course, you must forgive me, as I've never seen wiring in ducts (other than a short length to power something that was part of the duct system!).
300.21 and .22 seem to be the primary place where the NEC discusses wiring in ducts, with numerous other sections that boil down to "OK to run plenum rated wires in ducts." There ARE some other qualifications, so check it out.

Re: running cat5e #159805
02/01/05 08:25 PM
02/01/05 08:25 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Reno, I'm not smacking anyone....

It is a horrible practice in my opinion though. I've seen it done, even been forced by an employer to do it myself once. I don't like it at all.

Seen this thread for a day or so, but was reluctant to answer. Wish it were not an actual code.

[This message has been edited by e57 (edited 02-01-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15