#15831 - 10/30/02 11:55 AM Pool pump 220 or 110  
rayh78  Offline
Member
Joined: Nov 2001
Posts: 23
Have pool pump on 110v with a GFI breaker. Had heard it was cheaper to run as 220v. Is it worth it to rewire? 1 HP motor
Thanks


Work Gear for Electricians and the Trades

#15832 - 10/30/02 12:28 PM Re: Pool pump 220 or 110  
Joe Carpenter  Offline
Member
Joined: Dec 2001
Posts: 50
USA
No,it is not worth it. You pay for electriity in watts (power). If you run it at high voltage (240 volts)the amps will drop about in half. But for quick figuring, Volts X Amps = Watts.
So lets say your motor draws 10amps at 120 volts. that is, 10 x 120 = 1200 watts. Now lets say you hook it up to 240 volts and it draws only 5 amps now. That is 5 x 240 = 1200 watts. same thing.
Hope this helps. Have a safe and shockfree time in your pool!


#15833 - 10/31/02 06:43 PM Re: Pool pump 220 or 110  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
I was always taught to use the highest voltage rating on a motor nameplate when possible. Power savings (if any) is one reason, but, does the motor not run cooler (less stressed), last longer, and run more efficiently when hooked up 220 vs. 110?


#15834 - 10/31/02 09:35 PM Re: Pool pump 220 or 110  
Joe Carpenter  Offline
Member
Joined: Dec 2001
Posts: 50
USA
When the motor is set up for 110 volts the windings are connected parellel. When the motor is connected for 220, the windings are connected in series. Therefore internally on the windings you have the same voltages and current flows on each set of windings.
That's the basic gist of it. I'm not a motor specialist by any means. Perhaps someone with more experiance would like to elaborate.


#15835 - 10/31/02 09:57 PM Re: Pool pump 220 or 110  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Joe is correct. This sketch might help illustrate what he said.

[Linked Image]

Ed


#15836 - 10/31/02 10:03 PM Re: Pool pump 220 or 110  
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
Your motor will not be cheaper to run, but it will run more effeciently at the higher voltage. The higher the voltage the lower the ampacity.


#15837 - 10/31/02 10:31 PM Re: Pool pump 220 or 110  
jlhmaint  Offline
Member
Joined: May 2002
Posts: 202
Fredericktown, OH, U.S.A
As some have already stated lower amps

the key to the higher voltage is you get lower amp draw on a circuit so you can run smaller wire and conduit which reduces cost of install


#15838 - 11/01/02 08:40 AM Re: Pool pump 220 or 110  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Is the start winding on the second drawing supposed to be in series with a run winding?


#15839 - 11/01/02 01:50 PM Re: Pool pump 220 or 110  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Quote
Is the start winding on the second drawing supposed to be in series with a run winding?


Yes, it is. It is a 115 volt winding so has to be in parallel with one half of the run windings (for the high voltage connection).

The two run winding sections in series act as a voltage divider to split the 230 volts into two equal voltages of 115 each.

It will draw it's current through one of the run windings for a few seconds during starting, but that doesn't cause a problem.

All three windings are rated at 115 volts.

Ed
PS - These comments and the diagram refer to the basic general purpose motor. There are many other winding arrangements.

[This message has been edited by electric-ed (edited 11-01-2002).]


#15840 - 11/01/02 05:21 PM Re: Pool pump 220 or 110  
electrician02125  Offline
Member
Joined: Feb 2001
Posts: 89
The higher the voltage the less amperage equals smaller wire and OCP.

A little bit of savings I guess.


Page 1 of 2 1 2

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.8159 MB (Peak: 0.9884 MB) Zlib enabled. Server Time: 2017-07-27 14:51:13 UTC