Aluminum Romex #156060
03/09/05 09:53 PM
03/09/05 09:53 PM
D
denny3992  Offline OP
Member
Joined: Jan 2005
Posts: 53
orwigsburg,pa USA
Doing a remodel-renovation taking out 3 outlets(moving closets adding a bathroom) and adding new circuits pulled apart the receptacles and what did i see ??
Aluminum romex on a device marked CU only!

How have you fellas addressed telling a customer about the dangers of having this stuff in there homes? do you go the fire hazard route? or the they dont make it any more and the reason is... its junk?

any input ???

I just dont like the stuff and would not feel right by not telling them they have a possible hazard in there walls!!

Business, Office, Estimating, Legal:
Re: Aluminum Romex #156061
03/10/05 04:25 AM
03/10/05 04:25 AM
I
Indcom  Offline
Member
Joined: Jan 2005
Posts: 34
Katy, TX USA
I always inform the HO on the potential hazards of AL wiring in older homes. Give them as much info as possible so they can make an informed decision.

In the meantime- I offer them to either change the devices to CO-LAR rated devices or do the Purple Ideal wirenut route. (Which is more expensive @ about $3.00 per wirenut)

I don't beat them over the head with doing an entire wiring system upgrade and I try not to scare them into it either. Just give them fair warning and also tell them that you can't be held responsible for the existing wiring conditions.


John C. Harvey
IndCom Electrical Estimates
Re: Aluminum Romex #156062
03/15/05 09:01 AM
03/15/05 09:01 AM
K
kd  Offline
Member
Joined: Dec 2004
Posts: 52
The purple wire nuts have performed poorly in tests. To solve the problem without running new wire in the walls, it is a good idea to splice Copper onto the Aluminum so future devices can all be standard CU only. It is best to use splices that do not have the Aluminum touching the Copper. For a few splices use small split bolts with a Cu/Al seperator plate and with Deox. For lots of splices use the COPLAM system: crimps(Cu in one end, Al in the other)with a special crimp tool. Houses with Aluminum #12, #10 NM are many times more likely to have a major electrical fire. Talk to your fire dept!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,231
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,543 Are you busy
180,346 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.9506 MB (Peak: 1.0735 MB) Zlib enabled. Server Time: 2018-01-19 03:45:32 UTC