#154539 - 03/13/07 05:02 PM allied 1099 boxs  
big guy  Offline
Member
Joined: Dec 2003
Posts: 59
pa
HI
I am working on town homes and would like to know if the opening on a 1099 allied box should be sealed in a fire wall.

1099 boxs are 2hr rated but ones you put wires in the box there will be a open area around the wire.

If I do need to seal this box could I get the info that says that I have to do this.

thanks
matt


Building Codes & Related References

#154540 - 03/13/07 11:57 PM Re: allied 1099 boxs  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
If I read this right you need a putty pad to establish the fire rating


Greg Fretwell

#154541 - 03/14/07 07:12 AM Re: allied 1099 boxs  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,205
Chesapeake, VA
It sounds to me from that listing like the putty pads are only required if you don't meet the minimum separation of boxes. Am I reading that wrong?

The UL listing mentions several times that the gap between the box and the wall must be less than 1/8"- sounds to me like it's implying that some gaps less than 1/8" are acceptable, and cable entries may not need any special sealing.


#154542 - 03/14/07 02:08 PM Re: allied 1099 boxs  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
Yes you are right Steve. The joys of fire rated assemblies ;(

I was reading the wrong assembly description.


Greg Fretwell

#154543 - 03/14/07 04:05 PM Re: allied 1099 boxs  
big guy  Offline
Member
Joined: Dec 2003
Posts: 59
pa
I found it. thanks for the help


http://www.alliedmoulded.com/outlet_fireFAQ.cfm


#154544 - 03/18/07 12:52 PM Re: allied 1099 boxs  
Mark20  Offline
Member
Joined: Mar 2007
Posts: 25
Maryland
if you install 2 boxes in the same stud space of a dimizing wall-- one in "townhome a" and the other in "townhome b" then you would need putty pads for sure. as long as there's only one box in each stud space you shouldn't. at least that's how it's done in washington d.c. is that how everyone else sees it?



Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7767 MB (Peak: 0.9231 MB) Zlib enabled. Server Time: 2017-04-28 18:05:09 UTC