Electrical Room Doors #154095
03/25/04 08:28 PM
03/25/04 08:28 PM
N
Nick  Offline OP
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
I have a 1600A switchboard I am changing to a 2500A switchboard as part of the project I am doing. I just got the dimensions of the new board and it's quite a bit deeper than the existing one. The room has the required two exits. (As you face the board they are to your left an right.) The problem is the new board will protrude about 10" into the 4ft wide doors. The NEC only requires a 2ft wide egress so I am wondering if this violates a building code? [Linked Image]

Building Codes & Related References
Re: Electrical Room Doors #154096
03/25/04 08:54 PM
03/25/04 08:54 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Thats a great question, Nick.

In my opinion, the building code will probably only require one exit. With that in mind, I think you will be okay. If I were the inspector on this, I would pass it.

Strange scenario. Does any one else have anything to say about this?


Ryan Jackson,
Salt Lake City
Re: Electrical Room Doors #154097
03/25/04 11:00 PM
03/25/04 11:00 PM
K
kody wilson  Offline
Member
Joined: Mar 2004
Posts: 11
vancouver wa. 98664
where does nec call for a 2ft exit?

Re: Electrical Room Doors #154098
03/25/04 11:03 PM
03/25/04 11:03 PM
K
kody wilson  Offline
Member
Joined: Mar 2004
Posts: 11
vancouver wa. 98664
where does nec call for a 2ft exit?

Re: Electrical Room Doors #154099
03/25/04 11:29 PM
03/25/04 11:29 PM
S
stamcon  Offline
Member
Joined: Mar 2001
Posts: 330
So San Francisco CA
Kody, 600V or less 110-26(c) 99NEC.
Over 600V 110-33(a).

[This message has been edited by stamcon (edited 03-25-2004).]


Steve
Re: Electrical Room Doors #154100
03/26/04 08:57 AM
03/26/04 08:57 AM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
While it may not be an NEC violation, I don't have enough familiarity with BOCA to quote you on this.

Hey, when in doubt...

[Standard Reply]Check with your AHJ![/Standard Reply]

Re: Electrical Room Doors #154101
03/26/04 05:45 PM
03/26/04 05:45 PM
E
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
DougW's suggestion to check with the AHJ is probably the best answere. However, if I were making the call, I would probably agree with Ryan. Three points however: 1) The IBC, and I think all of the other building codes will require a 32 inch clear opening for egress doors. So, after subtracting the 10" protrusion, make sure you have a 32" clear opening. 2) I assume the protrusion is from the hinge side of the door? The switchboard will not interfere with the operation of the door handle? 3) I'm not sure what building code applies in your area, but this may be a technical violation of the provision in most buidling codes that there be a "landing" on both sides of the door. The landing needs to be the full width of the door (IBC doesn't say required width, just width) and should extend 44" from the door. The switch gear would technically be on the landing.

Re: Electrical Room Doors #154102
03/28/04 03:08 PM
03/28/04 03:08 PM
N
Nick  Offline OP
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Thanks for the replies. It will definatly be a AHJ call on this one. This is an OSHPOD job so I think I will submit an RFI with a drawing and let the Architect and OSHPOD hash it out. It will cost a fortune to relocate the switchboard or change the structure so it's out of my hands. I'll post the results when I get them.

(There is even bigger problems to deal with. The new 800A bypass isolation ATS won't fit in the room. [Linked Image] )

[This message has been edited by Nick (edited 03-28-2004).]

Re: Electrical Room Doors #154103
04/03/04 10:03 PM
04/03/04 10:03 PM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
How about changing the 48 inch door(s) to 36 inch door(s)?
Which condition exists (1, 2, or 3) and what voltage is the service?

Pierre


Pierre Belarge
Re: Electrical Room Doors #154104
04/13/04 10:15 PM
04/13/04 10:15 PM
N
Nick  Offline OP
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Update:
Met with the Architect and Electrical engineer today. We tossed around some ideas. Bottom line is the Architect says we can't reduce the ft door to ft and must have a 4 ft landing area ( like eprice stated). Now the first step is to see if the utility will allow a shallower pull section, meter/main. If not, the wall is going to have to move.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,552 Are you busy
180,359 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.005s) Memory: 1.0232 MB (Peak: 1.1984 MB) Zlib enabled. Server Time: 2018-01-19 18:56:29 UTC