photocell nightmare #15374
10/15/02 06:54 PM
10/15/02 06:54 PM
F
flush  Offline OP
Member
Joined: Dec 2001
Posts: 12
nj
hello all, i was called out on a job that an hid fixture wasnt working. i checked it out and the ballest was bad,also a pretty old fixture,the guy just wanted me to replace it ....a 220v hid fixture ran with 12/2. my question is doesnt a photocell need a neutral and what are my options any help would be apprecated ...thanks

Work Gear for Electricians and the Trades
Re: photocell nightmare #15375
10/15/02 07:25 PM
10/15/02 07:25 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Do they make a 220 volt photocell?

Re: photocell nightmare #15376
10/15/02 09:07 PM
10/15/02 09:07 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
intermatic has one. Don't have my catalog now but have used one about 7-8 months ago.


ed
Re: photocell nightmare #15377
10/15/02 11:36 PM
10/15/02 11:36 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
http://www.fisherpierce.com/N7700.htm
N7790 "105-285V" rating is prevalent in lighting controls.

Re: photocell nightmare #15378
10/16/02 04:28 PM
10/16/02 04:28 PM
F
flush  Offline OP
Member
Joined: Dec 2001
Posts: 12
nj
but my question is does all photocells need a neutral.. on a standerd photocell you have a black,red, and a white lead ....i dont have a neutral in the box. do they make a photocell that doest need a neutral?

Re: photocell nightmare #15379
10/16/02 05:00 PM
10/16/02 05:00 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
flush, please elaborate...do you mean are there 2-wire photocells? Not familiar with sny.

Re: photocell nightmare #15380
10/16/02 05:26 PM
10/16/02 05:26 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Flush - If you use a 240V photo control on at 240V fixture you do not need a neutral. The voltage rating of the photo control is the rating of the heater that controls the bi-metal switch. Most manufactures have 120V rated photo controls and 208V - 277V rated controls. As far as I know all of them have black, red and white leads. The black is line, red is the load and the white gets connected to the neutral on a 120V or 277V circuit or to the other line on a 208V or 240V circuit.

Curt


Curt Swartz
Re: photocell nightmare #15381
10/16/02 07:58 PM
10/16/02 07:58 PM
F
flush  Offline OP
Member
Joined: Dec 2001
Posts: 12
nj
ok great thanks for your help .

Re: photocell nightmare #15382
10/17/02 07:28 PM
10/17/02 07:28 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Here is where the electronic age gets tricky. If your device (photocell, timer, motion sensor, etc.) does not have a neutral wire, it is doing one of the following:
-letting a minute amount of current flow through your load (light) all the time; if this is the case, having more than one such device in the circuit will cause problems; or,
-the device uses the ground path as a neutral. If this is the case, the device will not work properly if the ground path is poor (or non-existent, as with k&t wiring).

Re: photocell nightmare #15383
10/17/02 08:08 PM
10/17/02 08:08 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
John

If the photo cell only has 2 wires then what you say is true about a minimum/maximum load. Most photo cells have 3 wires but the third wire does not have to be a neutral. If you are using the photo cell on a 120 or 277 volt fixture then the third (white) wire gets connected to the neutral but if the fixture is 208 or 240 volt then the third wire (still usually white) gets connected to the other line wire feeding the fixture.

Curt


Curt Swartz

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,548 Are you busy
180,358 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.004s) Memory: 1.0074 MB (Peak: 1.1822 MB) Zlib enabled. Server Time: 2018-01-19 17:37:19 UTC