#153572 - 10/20/03 06:43 AM Roof Mounted AC Units, Mechanical Code Rules?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]

NEC working space violations are clear, but what about the other systems used here, do they violate some other rules?

Also, how does the Mechanical Code cover the required rooftop receptacle and protection for the thermostat wires?


Joe Tedesco, NEC Consultant

Building Codes & Related References

#153573 - 10/20/03 12:22 PM Re: Roof Mounted AC Units, Mechanical Code Rules?  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Joe, I know it's common to see stat wire tied to the mechanical piping, and I've never heard of it being tagged.

Roger


#153574 - 10/20/03 01:24 PM Re: Roof Mounted AC Units, Mechanical Code Rules?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Roger:

That's true and is permitted by the NEC:

Quote
300.11(B)(2) Where the raceway contains power supply conductors for electrically controlled equipment and is used to support Class 2 circuit conductors or cables that are solely for the purpose of connection to the equipment control circuits


My question was related to a rule I remember being in the UMC calling for protection in a raceway.

Personally, I don't like seeing the thermostat wires installed as you describe, and as the code will permit, because it can be cut easily and may be the cause of a loss of life when someone is relying on AC or Heat to stay alive. That's one of the reasons why those circuit cannot be put into the same raceway as described in the reference in the FPN to 300.3(C)(1) .....


Joe Tedesco, NEC Consultant


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 