#152046 - 10/30/03 01:05 PM Ground Detectors  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,439
NY, USA
[Linked Image]

[Linked Image]

[Linked Image]
Quote
This is an old ground detector. The 230 volt bulbs are paired in series, 2 per phase, for used on the 480 volt system.

-Electure


Tools for Electricians:

#152047 - 10/30/03 10:06 PM Re: Ground Detectors  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Please explain what this is for--I don't quite follow. If a circuit came in contact with a ground, would it not trip the OCPD?


#152048 - 11/01/03 08:55 AM Re: Ground Detectors  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
TG,
It would be used on an UNGROUNDED system, in this case 480V delta.

In such a system a single ground on one phase would not trip out an OCPD (but a second, simultaneous ground on another phase might).

As the first unintentional ground might otherwise go unnoticed, the ground detector is fitted to provide an indication of a ground fault.


#152049 - 11/01/03 05:19 PM Re: Ground Detectors  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Ungrounded-delta {or even ungrounded-wye} plant distribution has a successful history for process-interruption minimization, but if you don’t act quickly after first fault, it gets messy—potentially with two or more overcurrent devices operating simultaneously. If you want to research this further, there is a {rare} online paper about it — www.neiengineering.com/papers/paper1JN.pdf for applying such a system one has to be well aware of the first-fault limitation and the need for action when it occurs. It is very problematic if one transformer set feeds two different areas of a plant, or worse yet, two different facilities under different ownership. The tradeoffs have to be carefully understood by all when adopting this system-grounding method.

There is understandable reluctance for many utilities to provide this type of service for their customers because its limitations have to be well understood by all to be effective. It is more likely found in cases where a facility buys power from the utility at medium voltage, or “primary” service, and the plant has complete control over all distribution and loads connected to the {typically 480V or 600V ungrounded-∆} system. If the utility owns the [480-600 or up to 4160V] secondary windings—essentially the grounding “source”, then it may be a poor choice from a reliability and service-continuity standpoint. There will be regional practices and local customs, but in many cases utilities flat out refuse to serve anything except for [480Y/277V or 600Y/347V] 4-wire grounded-wye service to limit repeated ‘rat-race’ complaints and finger-pointing from their customers.

If in the case where [phase-to-neutral loads are served, like 277- or 347-volt lighting loads] the distribution system must be solidly grounded. An absolutely insane stopgap mutation in system grounding is a corner-grounded-delta arrangement, except possibly for an isolated single-transformer/single-motor configuration, for all too often that seems to cause its own set of headaches.


#152050 - 11/01/03 05:47 PM Re: Ground Detectors  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
electure — The book page with the nippled lamps and horseshoe filaments really points out the antiquity of the system, and matches well with the apparent age of the switchboard. [Never mind the broken lamp with its handy 480V exposed-live parts.]

[Linked Image]

There is a lot of this type of stuff still in service out there—however ancient, misunderstood and neglected. It’s not hard to imagine a painter tipping a ladder up to the switchboard and planting a kneecap into the broken lamp.


#152051 - 11/01/03 09:02 PM Re: Ground Detectors  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Thanks for the great explanations, gentlemen!

Quote
kneecap into the broken lamp

OUCH!!!


#152052 - 05/07/04 10:35 PM Re: Ground Detectors  
Inspector Grump  Offline
Member
Joined: Jan 2003
Posts: 18
Bloomfield,NJ,USA
Us old guys worked with that fine equipment daily, we had digital wooden box meters!


Larry


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.7846 MB (Peak: 0.9359 MB) Zlib enabled. Server Time: 2017-04-23 11:49:12 UTC