#150542 - 06/18/05 03:52 AM Link to- Electrical Safety Handbook  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Guys,
Have a look at this.
It's right here .
Bill provided a link that you will see in his post.
For those of you that are interested in Workplace safety, get this!.


Let's face it, these days if you're not young, you're old - Red Green grin

Arc Flash PPE Clothing, LOTO & Insulated Tools

#150543 - 06/18/05 08:04 PM Re: Link to- Electrical Safety Handbook  
gideonr  Offline
Member
Joined: Dec 2004
Posts: 161
Edinburgh, Scotland, UK
Interesting how it suggests fuses (proper ones, not rewireable) protect so much better than mechanical circuit breakers.


#150544 - 06/24/05 03:29 AM Re: Link to- Electrical Safety Handbook  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Gideon,
Quote
Interesting how it suggests fuses (proper ones, not rewireable) protect so much better than mechanical circuit breakers.

HRC (High Rupturing Capacity) Fuses have a lot higher capacity than circuit-breakers, as far as High Energy Faults go.
Where as a Circuit-Breaker will interrupt "destructively" under Fault-Arc conditions, a Fuse package by design, will contain the entire arc within itself.
With the use of fine Silica sand, it forms glass under the heated conditions.
A lot better insulator.
Anyone else got any comments on this document?.


Let's face it, these days if you're not young, you're old - Red Green grin

#150545 - 06/24/05 10:18 AM Re: Link to- Electrical Safety Handbook  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
My understanding is that fuses have similar interrupting ratings as circuit breakers. If a overcurrent protective device needs to clear a arc fault, sometimes a circuit breaker will operate first if the arc fault current is below the current limiting range of the fuse. There are very few distribution systems that would benefit from a fuse rated at 300,000AIC, as the systems have fault duties much less than 200,000A.
The referenced safety book has excellent information, but you need to consider the source is only a fuse manufacturer.

[This message has been edited by Ron (edited 06-24-2005).]


Ron

#150546 - 06/25/05 06:42 AM Re: Link to- Electrical Safety Handbook  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Ron,
Quote
The referenced safety book has excellent information, but you need to consider the source is only a fuse manufacturer.

So going by that, should we disregard any Safety stuff put out by manufacturers of related equipment?.
In my opinion, there are a LOT of other things in this document, besides fusing.
I've never used Bussmann products, nor am I likely to.
I just thought that it was nice that they bought a thing like that out.


Let's face it, these days if you're not young, you're old - Red Green grin


Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7704 MB (Peak: 0.9087 MB) Zlib enabled. Server Time: 2017-07-25 16:55:50 UTC