Pay Careful Attention! Don't Let this Happen to You! #149928
06/05/04 08:04 AM
06/05/04 08:04 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]
[Linked Image]
[Linked Image]
Courtesy: ERI


Joe Tedesco, NEC Consultant
Arc Flash PPE Clothing, LOTO & Insulated Tools
Re: Pay Careful Attention! Don't Let this Happen to You! #149929
06/06/04 12:47 AM
06/06/04 12:47 AM
C
Crowbar  Offline
Member
Joined: Jan 2003
Posts: 33
Pittsburgh, PA,USA
Good thing he was wearing gloves!

Re: Pay Careful Attention! Don't Let this Happen to You! #149930
06/06/04 07:49 AM
06/06/04 07:49 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Yes, but you should see his face!

Terrible burns, and permanent disfigurement.

Interested persons can ask me for copies of the images via email ...


Joe Tedesco, NEC Consultant
Re: Pay Careful Attention! Don't Let this Happen to You! #149931
06/06/04 11:22 AM
06/06/04 11:22 AM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
I think the thing that would have exploded would be that control transformer! You can read the original diagram that shows that it is a standard 240/480 primary type.. [Linked Image]

Re: Pay Careful Attention! Don't Let this Happen to You! #149932
06/06/04 01:03 PM
06/06/04 01:03 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Siding with NJel, the ‘2300’ label must have been a ‘prop.’ Looks like the upper wiring is {SIS} 600V-class, and those hosed-up oversized crimp terminal are king of pathetic. The visisble CPT termainls do not apprear to have adequate creep and strike clearances for 5kV-class components.

OTOH, the star character should have had to defeat a mechanical door interlock to get into a live situation. [That 60%-polyester laundry-service shirt will now have emergency burn-unit workers cussing while trying to separate molten fabric from skin on his chest.]

For 600V-class work and instruments, serious consideration should be given to "IEC 1010-1" overvoltage-/installation-category numbers.




[This message has been edited by Bjarney (edited 06-06-2004).]

Re: Pay Careful Attention! Don't Let this Happen to You! #149933
06/06/04 06:26 PM
06/06/04 06:26 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Very sharp eyes, and thanks for the comments. This was a video and I sent the editor the link to this page. The video is a good one though, but not for real, of course, just actors!


Joe Tedesco, NEC Consultant
Re: Pay Careful Attention! Don't Let this Happen to You! #149934
06/06/04 06:56 PM
06/06/04 06:56 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Just as an aside guys.
Wouldn't a transformer like this have to be fitted with a shroud on them bare terminals?
Or even just a cover to prevent shocks when working around other equipment in the same panel?.

Re: Pay Careful Attention! Don't Let this Happen to You! #149935
06/06/04 10:34 PM
06/06/04 10:34 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
IEC-like ‘fingersafe’ terminal covers are a comparatively new addition for UL/ANSI industrial-control equipment. They are typically available as an aftermarket accessory, so there will be a lot of equipment that will not ‘catch up’ for awhile.

The get the impression that in North America is that, if the cabinet door is opened, only qualified people familiar with shock and short-circuit hazards should be working on it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,425 Re: Forum
170,876 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9930 MB (Peak: 1.1561 MB) Zlib enabled. Server Time: 2018-01-24 11:42:10 UTC