ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by gfretwell. 09/18/17 08:17 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 09/15/17 11:37 PM
Recreational Trailer Power Supply
by David1. 09/14/17 01:55 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,814 Are you busy
176,573 Re: Forum
168,503 Need opinion
Who's Online Now
1 registered members (annemarie1), 64 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#149859 - 05/01/04 11:41 AM Look before you "bleep#%#%%"  
rad74ss  Offline
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
Setting:

HVAC lab. Last year several safety devices were installed. E-Stop for main and control voltage at the distribution panels for each work station, along with remote toggle switches to turn main and control on/off at the unit. Strobe lights were placed at each station to indicate if any power was being used at the station.

After testing the unit the technician began to disconnect the power leads to the unit. The remote switch is a box with two toggle switches with push to test lights cord mounted back to the panel.

The cord was draped over the units enclosure door with the switches out of view of the tech. He reached over the door and hit the switches. Or so he thought. The audible click was the 120/240 switch. Without verifying the power was off he began to remove the 460 main wires. L2 and L3 came off without touching anything. L1 hit the units panel board.

The Arc caused first and second degree burns on his right hand. Luckily he just received flash burns and did not get shocked. The main terminal block blew completely off the panel. The main fuse blocks fuses blew off. One is embedded in the sheetrock and we can't find the other two. The contactor nearest the point of impact shattered on the inside. The coil was broken in three pieces.

Good news? Now the technician will only use the E-stops on the distribution panel itself. Not only is he sure the power is off, he has to face the strobe and ammeters when he does it. We have also started to place blinders on either side of each work station due to the fact that we noticed when more than one strobe was going you couldn't tell if it was the one in your station unless you looked directly at it. The metal enclosures and abundance of vaccum and charging piping caused so many reflections it was impossible to know if it was your strobe or the next guys over if you had your back to the light.

Lesson well learned.

Robert


Arc Flash PPE Clothing, LOTO & Insulated Tools

#149860 - 05/07/04 08:25 AM Re: Look before you "bleep#%#%%"  
n1ist  Offline
Member
Joined: Feb 2002
Posts: 183
Malden MA
It sounds like they need to implement and requre lockout/tagout in that lab before someone gets killed. Looking for strobes isn't good enough - what happens if the strobe is dead or a contactor gets welded?


#149861 - 05/07/04 11:38 AM Re: Look before you "bleep#%#%%"  
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
"The Arc caused first and second degree burns on his right hand. Luckily he just received flash burns and did not get shocked. The main terminal block blew completely off the panel. The main fuse blocks fuses blew off. One is embedded in the sheetrock and we can't find the other two."

That 480v power is just not very forgiving. The good news is no one got killed.

GJ


#149862 - 05/07/04 12:54 PM Re: Look before you "bleep#%#%%"  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The use of "e-stops" is not permitted for lockout purposes, the actual disconnect or breaker that feeds the power to the circuit must be locked open. Also you must always test the circuit with a tester that is known to be functional before working on the circuit even when it has been locked out.
Don


Don(resqcapt19)

#149863 - 05/08/04 06:37 AM Re: Look before you "bleep#%#%%"  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,222
SI,New Zealand
Darned good point Don!.
Using an E-stop as a means of isolation, is stupid to say the least!.
What ever happened to good ol' Voltage Indicators proving that the circuit was de-energised?.
Control Circuits are always live, at least up to the first NC contact, this could be an E-stop that you are working on!.
Be aware!. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin


Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.004s) Memory: 0.7704 MB (Peak: 0.9081 MB) Zlib enabled. Server Time: 2017-09-19 16:59:26 UTC