Grounding w/o a water pipe #14682
09/28/02 12:44 PM
09/28/02 12:44 PM
F
falcondfb  Offline OP
Member
Joined: Sep 2002
Posts: 37
Jersey, USA
the service is as such:
residential 200A overhead, seu drop to meter pan, pvc nip to nema 3r breaker enc, 4 cond seu to main lug panel in house.
there is a well with plastic piping into house, and since this is my first install where city water piping doesn't exist i'm not sure how to ground the system. I drove 2 g/r w/ the usual #6 but i'm don't think that is enough. Please shed some insite

Work Gear for Electricians and the Trades
Re: Grounding w/o a water pipe #14683
09/28/02 01:01 PM
09/28/02 01:01 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
You're done!! You must bond the water pipe to the service. If you like, you can catch the water pipe on the way to the ground rods, or run a separate conductor out of the service to catch it.

Suggest - bond around fiberglass collar on ductwork at unit.

Re: Grounding w/o a water pipe #14684
09/28/02 02:37 PM
09/28/02 02:37 PM
E
Electra  Offline
Member
Joined: Jul 2002
Posts: 38
Portland, Oregon, USA
Here in Oregon, if this was new construction, a ufer ground would also be required.

Re: Grounding w/o a water pipe #14685
09/28/02 02:50 PM
09/28/02 02:50 PM
A
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
Might want to check your GEC w/ 250.66. Think you'll need a #4 copper for the 200A service.

[This message has been edited by arseegee (edited 09-28-2002).]

Re: Grounding w/o a water pipe #14686
09/28/02 02:59 PM
09/28/02 02:59 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
arseegee,
As long as the GEC is only going to a rod, #6 is the largest that the code requires. See 250.66(A).
Don


Don(resqcapt19)
Re: Grounding w/o a water pipe #14687
09/28/02 04:29 PM
09/28/02 04:29 PM
A
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
Don, has this changed for 2002, I was taught that if a driven rod is your only GE then you size the GEC from the table. I thought you only used #6 if the rod was a supplemental electrode... guess I'm confused.

Re: Grounding w/o a water pipe #14688
09/28/02 05:09 PM
09/28/02 05:09 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
arseegee,
No change in the code rule, however in the '96 and earlier codes this rule was Exception #1(a) to 250-94. The rod really isn't a very good electrode and it will never carry very much current into the earth. A #6 is more than enough copper to carry the current that the rod can put into the earth and that is why the rule exists. There is no electrical advantage to installing a larger GEC to the rod.
Don

[This message has been edited by resqcapt19 (edited 09-28-2002).]


Don(resqcapt19)
Re: Grounding w/o a water pipe #14689
09/29/02 11:14 AM
09/29/02 11:14 AM
F
falcondfb  Offline OP
Member
Joined: Sep 2002
Posts: 37
Jersey, USA
thanks for the replys, i had all the same thoughts but wasn't sure which way to go. i wish i had gotten a rod under the basement floor


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,890
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
Potseal 15
sparky 15
Popular Topics(Views)
243,565 Are you busy
180,366 Re: Forum
170,843 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.004s) Memory: 0.9903 MB (Peak: 1.1484 MB) Zlib enabled. Server Time: 2018-01-20 17:00:15 UTC