Looking for AFCI opinions #14374
09/20/02 10:13 AM
09/20/02 10:13 AM
P
Pearlfish  Offline OP
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
Okay guys, I need your opinions. I have a customer who is converting some attic space into an storage area. She had the rafters covered over with floorboards, and wants me to install some lighting and an exhaust fan. Since the area is all DRY exposed wood, and will be filled with cardboard boxes. I feel this would be a good place to utilize an AFCI breaker. What are your opinions? Would you spend the extra money?

Work Gear for Electricians and the Trades
Re: Looking for AFCI opinions #14375
09/21/02 06:13 AM
09/21/02 06:13 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
Why, if your wiring methods are to code ?

Re: Looking for AFCI opinions #14376
09/23/02 01:14 PM
09/23/02 01:14 PM
P
Pearlfish  Offline OP
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
I have to come back with the question "If bedrooms are wired to code, why do they now require AFCI breakers"? In a bedroom the wiring is located within walls that are covered with 5/8" sheetrock (here in Cook County, Illinois). In my application, the area surrounding my installation is all bare wood. The underlayment of the roof, the roof joists, the ceiling joists below as well as the new OSB that was laid on top of them. As well as all the cardboard boxes the homeowner will be storing in the general area. An area that might not be accessed for months at a time.

Maybe I'm thinking too deeply into this, Or maybe I've been reading too many of Mike Holt's newsletters. I just wanted to raise a topic of discussion. And get an educated opinion from my peers.

Thanks in advance,
Steve

Re: Looking for AFCI opinions #14377
09/23/02 05:58 PM
09/23/02 05:58 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
Pearlfish,

Are you using an AFCI to protect NM in an area of exposure to damage?

Quote
I have to come back with the question "If bedrooms are wired to code, why do they now require AFCI breakers"?


you make my point for me......

Re: Looking for AFCI opinions #14378
09/24/02 09:51 AM
09/24/02 09:51 AM
P
Pearlfish  Offline OP
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
NO, here in the Chicago area, the only game in town is THHN in 1/2" EMT. My work is all mounted overhead.

Re: Looking for AFCI opinions #14379
09/24/02 04:08 PM
09/24/02 04:08 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Another point strikes me on this. If an AFCI is necessary to guard against arcs that may occur at joints feeding bedroom receptacles, why does the NEC not require AFCIs on all the other circuits that may also pass through bedroom walls? (e.g. tA circuit feeding an adjoining room.)

Re: Looking for AFCI opinions #14380
09/24/02 07:18 PM
09/24/02 07:18 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
a good ,and overlooked point Paul,
as the AFCI breaker is listed primarily for branch circuit protection, and not beyond the outlet....

Pearlfish,
then what is it that would suggest added protection?

Re: Looking for AFCI opinions #14381
09/24/02 09:48 PM
09/24/02 09:48 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Pearlfish
Since AFCIs are not listed as tested with anything but romex, and you already are protected with EMT, I would not waste money and buy an AFCI.
You will not be increasing safety enough to warrent the cost.


ed
Re: Looking for AFCI opinions #14382
09/25/02 06:14 AM
09/25/02 06:14 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
Pearlfish,
we in Vermont have been a code cycle ahead of the nation (210.12).

at first i did many service upgrades with AFCI's pedaling them to customers as a fail safe for older wiring , in that they need fear no arc again.

of late, all the fallicies and inconsistencies have surfaced, i no longer advocate them as a 'bandaid' for older wiring, or any that would be installed in the grey 'exposed' area.

here's one....

compare GFCI's to AFCI's in the sense of survivability, read Mr. Ken Silerstien's article on page 150 of the Sep. 02' Electrical Contractor mag....

I had seen that GFCI's had many ROP's in the last cycle to this end,( probably it went some cycles back) inspectors etc had seen many malfunction in the field....

note most are not proximal to the panel,( as AFCI's) where voltage variants/sags/swells/spikes, and all form of dirty power will occur....

one would think .....good for the goose/good for the gander

???


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,513 Are you busy
180,304 Re: Forum
170,802 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.003s) Memory: 0.9993 MB (Peak: 1.1668 MB) Zlib enabled. Server Time: 2018-01-16 19:19:31 UTC