AC insulation resistance tester #143132
05/12/05 06:13 PM
05/12/05 06:13 PM
L
lyledunn  Offline OP
Member
Joined: Jun 2002
Posts: 159
N.Ireland
Have any of you guys used an ac insulation resistance tester?


regards

lyle dunn
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: AC insulation resistance tester #143133
05/12/05 08:22 PM
05/12/05 08:22 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Yes lyle,
I use one every once in a while here.
I take it that you are talking about a Hi-Pot test (or Dielectric Withstand Test), as opposed to the plain-vanilla DC Insulation Resistance test?.

Re: AC insulation resistance tester #143134
05/14/05 07:26 AM
05/14/05 07:26 AM
L
lyledunn  Offline OP
Member
Joined: Jun 2002
Posts: 159
N.Ireland
Yes Trumpy, thanks for the reply.
I know that they are required for dielectric testing of certain products and electrical systems. An output of 3750vac even though current limited is not appropriate in the wrong hands.
What I wanted to know was if these instruments had a place in the field rather than in the production line lab.


regards

lyle dunn
Re: AC insulation resistance tester #143135
05/14/05 08:16 AM
05/14/05 08:16 AM
C
chipmunk  Offline
Member
Joined: Jul 2004
Posts: 144
Southampton, UK
Way back in the last century, (ok 12 years ago) I had to use such a beast as part of the portable appliance testing regime where I worked. Output as you say, up to 3750 volts AC, current limited to 5/10/15 mA, selected by a switch, with a deeply recessed "operate" button so it couldn't be energized accidentally. I agree they should only be used by competent persons trained in the dangers of high voltage.
With a probe carrying that kind of voltage, you could do a lot of damage to some kinds of electronic devices. But it helped pick up deteriorating insulation on double insulated tools and appliances, so yes, I believe they do have a place in the field, just a very narrowly defined one.

Re: AC insulation resistance tester #143136
05/18/05 08:05 AM
05/18/05 08:05 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Lyle,
We have a 20kV model here at the PoCo, it's used for flash testing HV cables, transformers and switch-gear, as well as the odd suspect bushing insulator.
I agree fully with yourself and Chipmunk, 3.75kV is not the sort of cat you want to let out of the bag, these voltages are lethal with the most minute of current levels. [Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,515 Are you busy
180,312 Re: Forum
170,808 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 14 (0.007s) Memory: 0.9661 MB (Peak: 1.1052 MB) Zlib enabled. Server Time: 2018-01-17 05:09:06 UTC