EARTHING #141499
08/26/04 05:04 PM
08/26/04 05:04 PM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
If i was asked to test some buildings to determin whether the Ze was to comply (dependent on the type of supply) and that i new there was no main bonding in the buildings (due to no water/gas services)would it be possible to take a Ze reading at a socket to see if the supply had a sufficent main earth.

i know the buildings installation should have already have been tested for this before they where energised!!!!!!!
also im not looking for exact figure just need to determine if they comply.

[This message has been edited by james S (edited 08-26-2004).]

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: EARTHING #141500
08/27/04 01:12 AM
08/27/04 01:12 AM
A
aland  Offline
Member
Joined: May 2004
Posts: 186
United Kingdom
No! technically ze is what it says the external loop so you need to switch off and disconnect the outgoing earth and measure the loop of the supply cable. If there is a difficulty with isolation why not do Zs at socket and then do R1+R2 measurment on the same final circuit, subtract your R1+R2 from Zs and that will give you an approximate Ze.
Hope it makes sense.
Alan

Re: EARTHING #141501
08/27/04 05:40 AM
08/27/04 05:40 AM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
i see your point aland but if you where to take a Zs test and the resistance reading was lets say 0.5ohms for a tn-s supply system, this system would comply and when you take your R1+R2 measurment and subtract it away from your Zs the initial reading obtained can only get better.

Re: EARTHING #141502
08/27/04 06:18 PM
08/27/04 06:18 PM
A
aland  Offline
Member
Joined: May 2004
Posts: 186
United Kingdom
James, your right, but in measuring ze you are trying to eatablish that there is a satisfactory external loop impedance. Dont forget that any zs measurment is likely to take the shortest possible path, exactly the same as an earth fault will, any fault will not travel the length of the cpc back to the dis board. If the building has a steel frame with metal conduit strapped to it it becomes a parallel path and will affect your readings, as will any water heaters or central heating connected. The only true way is to measure Ze with everything disconnected and then add R1+R2 to give you Zs. invariably the measured Zs will always be lower due to these parallel paths

Re: EARTHING #141503
08/28/04 08:30 AM
08/28/04 08:30 AM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
in my first post i stated that there is no main bonding, there for no parallel paths which means only the circuit cpc and external supply cpc are used for a return loop.
i appreciate your points made aland thanks for your input. [Linked Image]

Re: EARTHING #141504
08/30/04 05:09 AM
08/30/04 05:09 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Measuring Zs and then allowing for the cable impedance will give you a true value for Ze only if you can be absolutely certain that there are no parallel paths to earth anywhere.

The lack of bonded water/gas services is a start, but there are many other places where a parallel path could exist. Alan mentioned conduit strapped to building metalwork.

Even if wiring is run as T&E or in PVC conduit you could still have a metal-clad socket or switch box in contact with structural steel somewhere. If you want to be really picky, even a metal box screwed into mortar will offer some resistance to earth (O.K., admittedly any such resistance is likely to be so high as to be insignificant compared to Zs).

Re: EARTHING #141505
08/31/04 04:37 AM
08/31/04 04:37 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Good earthing is of up-most importance in any Electrical system.
Ze = the impedance of the Earthing system,
which should be of a very low value, to ensure that a large enough current flows under fault conditions.
Zs, on the other hand, gives the Impedance of all of the Supply side of the circuit.
Phase wires, the transformer winding(s), and the fusing through to the sub-circuit.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
sparky 22
Admin 20
Potseal 13
Popular Topics(Views)
243,531 Are you busy
180,336 Re: Forum
170,825 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 14 (0.007s) Memory: 0.9838 MB (Peak: 1.1356 MB) Zlib enabled. Server Time: 2018-01-18 08:01:44 UTC