looking for miniature circuit breaker #137021
05/21/03 08:15 PM
05/21/03 08:15 PM
J
Juan Carlos Moreno  Offline OP
Junior Member
Joined: May 2003
Posts: 3
Bogota - Colombia ( south Amer...
I´m looking for a three pole 120/240 rated m.c.c.b ( plug-in or cable-in/cable-out type) UL-489 certified in order to be used in a three phase 208Y/120 volts power system as main protection or feeder.

I´ve seen some products manufactured by Westinghouse/cutler-hammer but rated 240 (called "quick-lag").

Would you please inform me if you know any reference and manufacturer?

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: looking for miniature circuit breaker #137022
05/22/03 03:33 AM
05/22/03 03:33 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
JCM,
We use these(Quick-Lag) breakers in some types of Gael switchboards over here in NZ.
Just can't remember who makes them off-hand,
but I can find out for you at work tommorrow!.
These are rated 400/230 and I don't think that they are UL listed either.
BTW, welcome to ECN!!. [Linked Image]

Re: looking for miniature circuit breaker #137023
05/22/03 07:05 AM
05/22/03 07:05 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Hello Juan, and welcome to ECN.

As I'm in the United Kingdom, I'm not sure of the following, but these are my thoughts:

As the 120/240V system is a 3-wire single-phase service, does anyone actually manufacture a 3-pole breaker so rated?

I'm not sure what rating breakers would be used normally on an American 120/208 service, but I don't see any reason why a 3-pole unit rated for a plain 240V shouldn't be employed.

Could one of our NEC/rating experts in the States please comment?

Re: looking for miniature circuit breaker #137024
05/22/03 03:00 PM
05/22/03 03:00 PM
C
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Quote

As the 120/240V system is a 3-wire single-phase service, does anyone actually manufacture a 3-pole breaker so rated?


I know you know this Paul, but... If you have three transformers in delta configuration and ground at the center tap of one of them you get a 120/(208)/240V three phase system...

Re: looking for miniature circuit breaker #137025
05/22/03 07:32 PM
05/22/03 07:32 PM
J
Juan Carlos Moreno  Offline OP
Junior Member
Joined: May 2003
Posts: 3
Bogota - Colombia ( south Amer...
Thank you for your comments. However let me bring you additional information:The three-phase, four-wire power system I´m speaking is neither the " center-tap grounded delta" nor the " center-tap grounded open delta" but the " grounded Wye" as showed in the following address: http://home.att.net/~benmiller/elecsys.htm

As you realize the phase to ground voltage is 120 volts, not 208 volts.

Would you please bring me your additional concept after having clarified this point?

Re: looking for miniature circuit breaker #137026
05/23/03 04:16 AM
05/23/03 04:16 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
JCM,
In this particular case, I don't think that voltage comes into it.
As long as the voltage of the unit is above the voltage of the system in use.
3 pole breakers are generally supposed to trip if one of the poles break.
It shouldn't really matter what sort of system that this is done under!.
[Linked Image]

Re: looking for miniature circuit breaker #137027
05/24/03 07:03 AM
05/24/03 07:03 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
For a normal type of thermal/magnetic circuit breaker, the voltage rating is the maximum voltage that may be applied, either between phases or from phase to ground.

A 3-pole breaker rated at a straight 240V should therefore be suitable for use on a 208Y/120V system.

A GFI or AFCI would be a different matter, as the electronics rely on the supply being a certain level to operate properly.

Re: looking for miniature circuit breaker #137028
05/26/03 01:41 PM
05/26/03 01:41 PM
C
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
I'm surprised none of our friends from the States have responded.

The description of UL 489

This seems like an ordinary molded case circuit breaker. All of the manufacturs must carry them. Square D, Cutler Hammer, Siemens and others.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,558 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9929 MB (Peak: 1.1544 MB) Zlib enabled. Server Time: 2018-01-20 03:22:57 UTC