#136942 - 05/13/03 12:35 PM REFERENCE METHODS  
james S  Offline
Member
Joined: May 2003
Posts: 107
West England
WHAT REFERENCE METHOD IS USED IF YOUR METHOD IS NOT LISTED IN THE CURRENT CARRYING CAPACITY TABLES EG CABLES BURIED DIRECT UNDERGROUND ( WITH MECHANICAL PROTECTION OF COURSE).I CANT EVEN FIND IT IN THE MAIN REFERENCE METHOD TABLES!

WORKING IN ACCORDANCE WITH THE IEE REGULATIONS.


[This message has been edited by james S (edited 05-13-2003).]


Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#136943 - 05/13/03 01:21 PM Re: REFERENCE METHODS  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
James,

Welcome to ECN,
Is this a question about UK Regs? or US?

Bill

[This message has been edited by Bill Addiss (edited 05-13-2003).]


#136944 - 05/13/03 01:43 PM Re: REFERENCE METHODS  
james S  Offline
Member
Joined: May 2003
Posts: 107
West England
UK


#136945 - 05/13/03 02:59 PM Re: REFERENCE METHODS  
sanUK  Offline
Member
Joined: Jan 2003
Posts: 45
Scotland
There is no reference method for Cables buried underground, only in Enclosed trenches.

Most likley because there would not be any problems with heat dissipation under the ground, so no derating.

522-06-03 details requirements for a buried cable or conduit.


#136946 - 05/13/03 07:39 PM Re: REFERENCE METHODS  
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
The current carrying capacity of a cable buried directly is very high, in fact higher than cables clipped directly. The limit is likely to be when the cable it leaves the ground.

I don't have a UK reference, but I could try to dig up a Swedish reference. Or the some of our American friends could tell us what the NEC or CEC has to say.

Edit: I took the first reference that popped up. Swedish AXBJ, 5 conductor, aluminium 1kV cable.
Conductor 65°, air 25°C,
ground 15°C, depth 0,7 metres

Gauge.......50 95 150 240 sq.mm
In ground...160 230 295 385 Amps
In air......140 210 275 370 Amps

Just to give an example.

[This message has been edited by C-H (edited 05-13-2003).]


#136947 - 05/27/03 06:51 PM Re: REFERENCE METHODS  
lyledunn  Offline
Member
Joined: Jun 2002
Posts: 159
N.Ireland
Interesting point. I use AMTECH cable calculation programme. It states reference method 7 for your particular situation. Now I left my glasses at the caravan this weekend but I cant see ref method 7 in appendix 4. In any event I would be glad to calculate any circuit for you using the programme.


regards

lyle dunn

#136948 - 05/30/03 07:52 PM Re: REFERENCE METHODS  
james S  Offline
Member
Joined: May 2003
Posts: 107
West England
Thanks, much appreciated all!

[This message has been edited by james S (edited 05-30-2003).]


#136949 - 06/07/03 04:45 AM Re: REFERENCE METHODS  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,223
SI,New Zealand
Just wondering,
What is a reference method?.
Is this like a Current carrying capacity Table, in various types of installations?.


#136950 - 06/07/03 09:05 PM Re: REFERENCE METHODS  
sanUK  Offline
Member
Joined: Jan 2003
Posts: 45
Scotland
Quote
Just wondering,
What is a reference method?.
Is this like a Current carrying capacity Table, in various types of installations?.


Yes [Linked Image] you look up the Schedule of installation methods table first (4A1), to get the Method No, then refer the method Number to the current carrying capacity tables, also taking into account various correction factors.



Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.033s Queries: 14 (0.015s) Memory: 0.8004 MB (Peak: 0.9703 MB) Zlib enabled. Server Time: 2017-10-19 03:40:07 UTC