Smoky failure of a swiss receptacle #136809
05/06/03 02:00 PM
05/06/03 02:00 PM
T
Texas_Ranger  Offline OP
Member
Joined: Dec 2001
Posts: 2,407
Vienna, Austria
[Linked Image]

This picture was posted to de.sci.ing.elektrotechnik and I thought it might be interesting for you.
The OP tried to hook up a 2000W heater to the 250V/10A rated receptacle and the result can be seen on the picture. This was not a cheap receptacle but a real expensive one that even once won a design prize. All this happened twice with receptacles of the same brand.

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Smoky failure of a swiss receptacle #136810
05/06/03 02:37 PM
05/06/03 02:37 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Ranger,
Looks like there's been a fair bit of heat there.
A loose connection perhaps?. [Linked Image]

Re: Smoky failure of a swiss receptacle #136811
05/07/03 04:40 AM
05/07/03 04:40 AM
T
Texas_Ranger  Offline OP
Member
Joined: Dec 2001
Posts: 2,407
Vienna, Austria
I have no idea. As you can see this was a backstabbed (or in this case sidestabbed) receptacle. They're fairly common in Europe, and many electricians will tell you these are far better than screw terminals.
One guess in the original thread was that the terminals were rated for 2 conductors, but the spring pressure wasn't evenly distributed onto both wires, so one wire overheated. BTW, the more or less intact red wire is the phase jumper to the light switch above (not really visible in the pic). The badly burnt wire is the originally red feeder to the receptacle.
I once saw a switch that looked like that, it had a black sooth trail all above on the wall, about half a meter high. Story back then was that the switch had come loose from the box (a known fact) and some ingenious students stuffed firecrackers into the box and pushed the switch back in. However, a short seems more likely to me (this was a bell button with a light inside), even though I'm not sure how that could have happened. After some time the charred switch was removed and the wires were hanging loose in mid-air, in a highschool main entrance. Don't know whether they were hot.

Re: Smoky failure of a swiss receptacle #136812
05/07/03 09:22 AM
05/07/03 09:22 AM
S
swiss  Offline
Junior Member
Joined: Apr 2003
Posts: 4
Zurich
this is realy not a cheap one. It's made from www.feller.ch . I worked with them as an electrician in switzerland. It's good stuff.
But the same situation was happend twice at my parents house. I don't know why. It is a combined element with a switch on the top. The second wire you see is the phase (hot wire) who is bridged to the switch.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,527 Are you busy
180,329 Re: Forum
170,821 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.004s) Memory: 0.9586 MB (Peak: 1.0897 MB) Zlib enabled. Server Time: 2018-01-17 21:43:16 UTC