Fire or safety concerns about receptacle loads #13375
09/02/02 11:36 AM
09/02/02 11:36 AM
E
Elzappr  Offline OP
Member
Joined: Dec 2001
Posts: 270
Oregon
Art 210 requires stationary equipment that takes up 50% of a circuit's capacity to be a dedicated circuit. Other than engineering or usage convenience considerations, is there a safety issue? I recently had to repair a damaged installation that apparently was modified by a maintenance person AFTER initial construction, so that it violated the 50% rule. They tapped into a large role up door opener (in a commercial building) to provide power for a couple of convenience outlets. I don't like driving customers away by re-engineering existing installations because of code issues which aren't obvious safety issues. Anyone have some perspective about what is so dangerous about violating the 50% rule?

Work Gear for Electricians and the Trades
Re: Fire or safety concerns about receptacle loads #13376
09/02/02 02:41 PM
09/02/02 02:41 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
the fallicy is, that anyone can 'dedicate' a circuit without consultation......

Re: Fire or safety concerns about receptacle loads #13377
09/02/02 02:45 PM
09/02/02 02:45 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
As I see it, the problem with violating such a rule would be that if/when other high-power appliances are connected to the circuit, there could be a high incidence of nuisance tripping.

That in itself wouldn't be a problem so long as the OCPD and cables are properly sized. The only real safety issue I can see is that regular nuisance trips might lead to some uninformed person deciding to uprate the breaker in order to "solve" the problem. Then it could most definitely be a safety problem.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,515 Are you busy
180,312 Re: Forum
170,808 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.9495 MB (Peak: 1.0726 MB) Zlib enabled. Server Time: 2018-01-17 05:09:50 UTC