Ufer in dirt #13012
08/22/02 08:09 PM
08/22/02 08:09 PM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
would you find this acceptable? [instead of stubbing the ufer up through the foundation wall 12" above the bottom plate indoors,] stub the Ufer rebar out of the footing, outdoors exposed to the dirt and weather, with a typical ground rod connection made to this Ufer. pipes, conduits, and rods can be iron or steel, if the conditions are met in 250, but it seems to me that rebar doesn't really fit outdoors in a wet environment. i would expect it to rust and lose its value at the acorn or clamp connection. but we allow clamps to bond to galvanized water pipes and black iron gas lines outdoors, and you are supposed to scrape the coating off to make a good bond. go figure.

Work Gear for Electricians and the Trades
Re: Ufer in dirt #13013
08/22/02 09:47 PM
08/22/02 09:47 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
When we use the rebar as an ufer we clamp a piece of #4 bare copper onto the rebar and run it to the service location.


ed
Re: Ufer in dirt #13014
08/22/02 10:01 PM
08/22/02 10:01 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
I have to ask; what is a "ufer"???

HotLine1
John


John
Re: Ufer in dirt #13015
08/22/02 11:08 PM
08/22/02 11:08 PM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
ufer = concrete encased electrode

Re: Ufer in dirt #13016
08/22/02 11:55 PM
08/22/02 11:55 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Cindy

I would have a hard time accepting the exposed ufer connection for the reasons you are concerned about. As far as other piping I have never been required to scrape the galvanized coating off water piping and doing so would cause the plumber and plumbing inspector to have a fit. Black iron gas piping and fittings are not supposed to be installed where they are exposed to weather unless they are coated for protection. Again it would be a violation to remove any protective coating.

I would also not permit an acorn clamp to used to connect the grounding electrode conductor to the ufer. I have never seen one listed for this purpose and doubt there are any. Copper and steel should never be in direct contact with each other because of electrolysis. I don't have a problem with using standard brass or bronze clamps even thought most are also not listed for this purpose. I know most of the T&B U-bolt type ground clamps are listed for rebar.

Curt


Curt Swartz
Re: Ufer in dirt #13017
08/23/02 05:39 AM
08/23/02 05:39 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
i stub out the cu in pvc. should i assume the effort here is in keeping a continuous GEC?

'fingers' i'm told disipate a strike better than a single line (ampacity divides..) there is even a 'crow's foot' design for this...

here's a Ufer John, just did one @ 2200' on ledge.

Re: Ufer in dirt #13018
08/23/02 07:01 AM
08/23/02 07:01 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
We must live in a different world here in So CA.
The AHJ's will only accept 20'or > of GEC sized (or larger) Cu as a Ufer.
When bonded to the rebar, I do it with Cadwelds.
Galvanized water lines? Haven't seen one in years, except on old buildings. Just Cu.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,405 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9835 MB (Peak: 1.1354 MB) Zlib enabled. Server Time: 2018-01-23 12:01:07 UTC