#129516 - 04/05/05 07:28 PM motor disconnect question  
knopp  Offline
Junior Member
Joined: Jun 2004
Posts: 2
richmond, va
i have two 480 3 phase motors, the first is a 10HP (14FLA)and the second is a 30HP (40FLA) these two are to be fed from individual circuit breakers at a main lug panel and a fusible disconnect supplies the incoming power. how do you properly calculate for the correct size time delay fuses at the disconnect.


Tools for Electricians:

#129517 - 04/05/05 09:29 PM Re: motor disconnect question  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
How about 430.63, which would, in your case put you at 430.62?
40A x 175% = 70A
70A + 14A = 84A
84A + the lighting and appliance load on the panel = Time Delay Fuse size?

[This message has been edited by Redsy (edited 04-05-2005).]



Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,260
Joined: December 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7426 MB (Peak: 0.8608 MB) Zlib enabled. Server Time: 2017-07-24 00:53:25 UTC