#129431 - 03/18/05 11:22 PM ungrounded neutral need connected to earth?  
unsaint32  Offline
Member
Joined: Aug 2004
Posts: 15
eden prairie, MN, USA
I know that in an ungrounded system, the neutral conductor is not connected to the equpment grounding conductor. But, does the neutral conductor of an ungrounded system need to be connected to earth (to an electrode)? I am looking for the answer in the code book, but any answer'd be appreciated.


Tools for Electricians:

#129432 - 03/19/05 08:33 AM Re: ungrounded neutral need connected to earth?  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
No Neutral on a ungrounded system


#129433 - 03/19/05 01:47 PM Re: ungrounded neutral need connected to earth?  
unsaint32  Offline
Member
Joined: Aug 2004
Posts: 15
eden prairie, MN, USA
Can an ungrounded system in a health care facility serve 120v load therefore requiring to have a neutral conductor?


#129434 - 03/21/05 01:32 AM Re: ungrounded neutral need connected to earth?  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
On an Ungrounded system, there is no Intentional Connection of the system to Earth Ground (or to enclosures Intentionally Bonded to Earth Ground), through either a Solid Connection or an Impedance / Resistance.

This means there is no physical Bonding of the Power System
(such as the Secondary Side of the Transformer delivering AC Power from the Utility Company)
to the Earth Ground / Metallic Raceways and/or Enclosures.

The Metallic Raceways and Enclosures WILL be Bonded together, and connected to a Locally Established Grounding Electrode System, but the Power System will not be connected to these items - hence the System is "Ungrounded".

The Power System may, or may not, incorporate the use of a "Neutral Conductor" - depending on the configuration; but still no Conductor is Intentionally Grounded, and the System has no "Grounded Conductor".

The most common configuration used for Ungrounded Systems (at least in my area - So. Calif.) is the Ungrounded 3 Wire Delta. Voltages of 480 VAC and 600 VAC, but may be some 240 VAC systems out there too.

Although Grounding a System does not achieve any merit in normal performance, it does effect the stresses imposed on Insulation and such.
An Ungrounded system may have an extremely high Potential to Ground at different points along the system's connected Equipment - at times exceeding the nominal rated Voltage by maybe 3 times as high!
This is due to Capacitive Coupling effect between the Power System's Conductors and the Grounded surfaces / Equipment / etc.
A Grounded System (solidly or through an Impedance / Resistance), will stabilize the Potential to Ground, thus reduce the Insulation Stresses.

Much more to cover on this stuff, and other Members can explain much better than I, so feel free to reply for additional info.
Also check the Technical Reference Section for Schematics, additional information.

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#129435 - 03/21/05 03:39 PM Re: ungrounded neutral need connected to earth?  
unsaint32  Offline
Member
Joined: Aug 2004
Posts: 15
eden prairie, MN, USA
thanks scott for clearing that up. One questoin I had it then ..an ungrounded system have two disadvantages?
1. cannot obtain steady voltage because there is no voltage reference.
2. cannot dissiplate high surges inflicted on to the electrical system (say a lightning surge)


#129436 - 03/23/05 11:38 PM Re: ungrounded neutral need connected to earth?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Carefully differentiate between bonding, grounding and grounding electrode.

Please, please, please get a new, old, tattered or borrowed edition of Soares' Book on Grounding and Read It Cover To Cover—Over And Over until you begin to follow it. Plan to take thirty years or so thinking it over.    ;-)

Bonding (As expertly explained by resqcapt19) is minimization of potential difference through limiting touch·and·step voltage.

Nowadays, utilities typically provide three-phase service only as soldily grounded four-wire-wye, but continue to maintain existing three-wire ungrounded systems.

Below 1kV, sole ‘earth return’ [between made electrodes] can not be relied on for effectively low impedance for rapid clearing of overcurrent devices.

Grounding-electrode conductors, though, are needed for bulletproof continuity to the grounding electrode—as a critically important pair being a ‘dissipation sink’ for capacitively, inductively and resistively coupled transient overvoltage/overcurrent.




[This message has been edited by Bjarney (edited 03-23-2005).]



Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,809
Joined: April 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7786 MB (Peak: 0.9241 MB) Zlib enabled. Server Time: 2017-04-28 10:20:19 UTC