what really is an ungrounded system? #129419
02/28/05 03:58 PM
02/28/05 03:58 PM
U
unsaint32  Offline OP
Member
Joined: Aug 2004
Posts: 15
eden prairie, MN, USA
Q 1) What is the purpose of ungrounded system. Is it not to trip the circuit breaker when

the first fault occurs? (for more controlled deactivation?)

Q 2) In a grounded system, having one conductor connected to earth provides the reference

for steady voltages supplied to loads. How is stable voltage accomplished in an ungrounded

system?

Q 3) Actually, there is no such thing as an ungrounded system, right? (Because an ungrounded

system is capacitively grounded.. whatever that means)


Thanks for your answers

Sung

Tools for Electricians:
Re: what really is an ungrounded system? #129420
03/01/05 05:00 AM
03/01/05 05:00 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Sung,
Welcome to ECN, [Linked Image]
Most Electrical systems throughout the world have a reference to Earth.
This is mainly for Safety reasons.
It is so that there is a limit on the Line to Ground voltage.

Re: what really is an ungrounded system? #129421
03/01/05 07:20 AM
03/01/05 07:20 AM
P
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
I wouldn't trust an ungrounded system where the primary has a higher voltage than the secondary to be very stable. Impedance grounding is generally adequate for a one fault tolerant system. And you'd need that grounding point to set an alarm to know where there is a fault.

I wouldn't even trust an article 411 system (411.5(A) requiring it to be ungrounded) unless it is isolated with a grounded electrostatic shield between primary and secondary, or has 2 transformers with an intermediate grounded loop at the final secondary voltage.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,602 Are you busy
180,416 Re: Forum
170,873 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.005s) Memory: 0.9498 MB (Peak: 1.0731 MB) Zlib enabled. Server Time: 2018-01-23 21:53:01 UTC