what is current on load side of transformer? #129315
01/16/05 10:27 AM
01/16/05 10:27 AM
C
Clydesdale  Offline OP
Member
Joined: Nov 2004
Posts: 138
ok...you have a 120V 60W lightbulb...it draws .5 Amps...right? now if you have low voltage lighting.....say you have a 10:1 stepdown transformer(120:12) driving a 20W lightbulb, would it be drawing 1.7 Amps?

Tools for Electricians:
Re: what is current on load side of transformer? #129316
01/16/05 04:29 PM
01/16/05 04:29 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Yes, that will be the current on the secondary (12-volt) side of the transformer.

In a theoretically perfect transformer, the primary current would then be 10% of that, or 0.17A. (Primary voltage is 10 times secondary voltage, therefore for the same power secondary current must be 10 times the primary current).

In practice, the primary current will be a little higher due to losses in the transformer, and due to the circuit not being purely resistive.

Re: what is current on load side of transformer? #129317
01/16/05 07:18 PM
01/16/05 07:18 PM
C
Clydesdale  Offline OP
Member
Joined: Nov 2004
Posts: 138
thanks, pauluk...so is low voltage lighting more economical? do you get the same amount of lumens per watt?...for instance do you get the same amount of light from a 12V 30Watt bulb as you get from a 120V 30Watt bulb?

also..the circuit not being purely resistive...is the transformer inductive?

[This message has been edited by Clydesdale (edited 01-16-2005).]

[This message has been edited by Clydesdale (edited 01-16-2005).]

Re: what is current on load side of transformer? #129318
01/17/05 01:32 PM
01/17/05 01:32 PM
I
IanR  Offline
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
While low voltage lighting is safer I wouldnt say it it going to be more efficient.
While the lumins per watt would be about the same(assuming comparing the same type of bulbs ie incansecent, etc.) there is always going to be some power loss in the stepdown Xfrmr, the smaller ones are particularly lossy, as well as voltage drop in the cables.
Remember in order to make the same light output(ie power) the low voltage lighting will draw more current thus requiring heavier cable to combat voltage drop. So overall efficiency will sffer there.

Re: what is current on load side of transformer? #129319
01/17/05 05:05 PM
01/17/05 05:05 PM
C
Clydesdale  Offline OP
Member
Joined: Nov 2004
Posts: 138
yes, i understand that there will be more current on the load side...but since there is 10 times less current on the line side of a 10:1 stepdown transformer, wouldn't your electric bill reflect that? doesn't the meter read what the line side of the transformer is drawing?

Re: what is current on load side of transformer? #129320
01/17/05 06:21 PM
01/17/05 06:21 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
If we assume lightbulbs of similar efficiency in terms of lumens per watt, there is nothing to be gained by stepping down to low voltage. The primary xfmr current in the above example works out to 0.17A (ignoring xfmr losses), but if you had a 20W 120V bulb connected directly to the 120V line that too would draw 0.17A, so the meter would still register 20 watts of power being consumed.

As Ian pointed out, you would likely be running less efficiently due to the xfmr and copper losses.

I remember I actually had a hard time explaining a situation like this to somebody a couple of years ago. They had a hallway with two pendant lights, each containing a compact fluorescent, about 18 watts each.

They had bought two low-voltage spot assemblies, each with three 12V bulbs rated at about 50W each.

They were convinced that because they were low voltage it was going to save energy, when in fact they were planning on replacing 36W of fluoro lights with 300W of spots.

I fitted them as that's what they wanted there, but I'm still not sure I convinced them that the low-voltage lights were actually going to cost more to run.

Re: what is current on load side of transformer? #129321
01/17/05 08:04 PM
01/17/05 08:04 PM
C
Clydesdale  Offline OP
Member
Joined: Nov 2004
Posts: 138
ok..i totally see it now, because if you divide 60W by 120V you get 1/2A ...but if you divide 60W by 12V you get 5A, on the line side of that it's still 1/2A...totally understand! thanks!pluss the inefficiency of the Xfrmr will burn up more $$$$$!!..ok ...next question, why then do all these companies make their low voltage lights so much more fancy/expensive and have more of a selection?..only for safety? (not to be undermined of course)
easy to market to people who think they are saving power?
[This message has been edited by Clydesdale (edited 01-17-2005).]

[This message has been edited by Clydesdale (edited 01-17-2005).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,406 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.005s) Memory: 0.9837 MB (Peak: 1.1379 MB) Zlib enabled. Server Time: 2018-01-23 14:00:50 UTC