corner grounded delta transformers #129228
11/20/04 06:13 PM
11/20/04 06:13 PM
L
lagunavolts  Offline OP
Junior Member
Joined: Mar 2004
Posts: 7
rancho santa margarita, CA. Am...
Can somebody explain how a corner grounded delta transformer works? Or does anyone know of any sites that give schematics??/

Tools for Electricians:
Re: corner grounded delta transformers #129229
11/20/04 09:11 PM
11/20/04 09:11 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Lagunavolts:

Quote

Can somebody explain how a corner grounded delta transformer works?


The Corner Grounded Delta system is a 3Ø 3 Wire configuration, of which has one of the Secondary output Lines (AKA "Phases") intentionally connected to "Ground" via the Grounding Electrode System.
Similar to the methods used to Ground all other Solidly Grounded AC Power Systems, the "Corner Grounded" Delta has Ungrounded and Grounded Conductors, plus Equipment Grounding / Bonding Conductors.

Think of the method "Normally" done to Ground the Secondary side of any Transformer (when planning to have a Solidly Grounded AC System from the Secondary).
If the Transformer is a Single Phase 3 Wire output, the Center Tapped "Neutral" Terminal (X0) is "Grounded", and this Conductor becomes the Grounded Conductor.
If the Transformer has a Three Phase 4 Wire Wye connected Secondary, the Common Star Point - also "X0", is "Grounded" and the Conductor Terminated to it is the System's Grounded Conductor.

With the Corner Grounded Delta, everything is quite the same as shown in the examples above. Only on this system, the differences are:
<OL TYPE=1>

[*] One of the "Normally" Ungrounded "Phases" will be Grounded - and thus become the System's Grounded Conductor,

[*] This is a "Single Voltage System" in simpler terms - only one Voltage is found between Phase Lines or Line and Ground,

[*] There is no "X0" Terminal,

[*] There is no "Neutral" Conductor,

[*] Single Phase 2 Wire or 3 Phase 3 Wire Circuits are available for use - but all are the same Voltage,

[*] Two of the "Phase Lines" will have full rated system Voltage to Ground, and one "Phase Line" will be Zero Volts to Ground.
</OL>

Choose one - and only one Line to become the Grounded Conductor, and perform Grounding Techniques as commonly done on other Grounded systems (GES, Bonding, etc.).

An example:

3Ø Delta / Delta Isolated Transformer.
Primary = 4160 VAC 3Ø Delta,
Secondary = 240 VAC 3Ø 3 Wire Delta.
Secondary Terminal "X1" = ØA,
Secondary Terminal "X2" = ØB,
Secondary Terminal "X3" = ØC.

GES and Equipment Bonding is connected to Terminal "X3" - or ØC.
This makes ØC the System's Grounded Conductor. Color Code for this Conductor = White.

Voltages are as follows:
A-B: 240 VAC,
A-C: 240 VAC,
B-C: 240 VAC,
A-G: 240 VAC,
B-G: 240 VAC,
C-G: 0 VAC.
("G" = Ground / Equipment Grounding Conductor / Grounded Conductor).

Now to the 2nd question:

Quote

Or does anyone know of any sites that give schematics??


I know a very familiar site with "A Few Schematics", and luckily there are a few Schematics of the Corner Grounded Delta.
The site is closer than you think! - in fact... you are at the site! Just missed the Schematics area by one forum down!

Click on a link below, which will open a new Window with Schematics for viewing and printing:
(Be sure to click on the underlined colored text to open the link)

Corner Grounded 3Ø 3 Wire Delta

3 Phase Delta Transformer Schematics

Menu for Technical Reference Section

The last link opens the Technical Reference area's "Menu" - from which you may use to search topics of the area in one page.

Good luck!
Let us know the outcome!!!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: corner grounded delta transformers #129230
11/21/04 09:11 AM
11/21/04 09:11 AM
L
lagunavolts  Offline OP
Junior Member
Joined: Mar 2004
Posts: 7
rancho santa margarita, CA. Am...
Scott,

thanks for the valuable detailed info on this delta system. I have never had this situation in front of me and in a couple of weeks i have to hook up this type of xfmr. I will study your info and I already have follow up questions. I will post back later.

thanks
jim

Re: corner grounded delta transformers #129231
11/27/04 01:11 PM
11/27/04 01:11 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
lagu—

Is the corner-grounded transformer in a new or existing application?

There are some cautions on overcurrent-device application.

Re: corner grounded delta transformers #129232
11/29/04 07:33 PM
11/29/04 07:33 PM
L
lagunavolts  Offline OP
Junior Member
Joined: Mar 2004
Posts: 7
rancho santa margarita, CA. Am...
this xfmr is being added in an existing bldg. I don't have all the spec's yet but will shortly. I will post back with more info.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,583 Are you busy
180,379 Re: Forum
170,856 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.005s) Memory: 0.9697 MB (Peak: 1.1096 MB) Zlib enabled. Server Time: 2018-01-21 22:30:09 UTC