Quick wire size question. #12897
08/20/02 10:22 PM
08/20/02 10:22 PM
E
Electric Eagle  Offline OP
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
Help! I'm working on a bid and my "handy" electric calculator is giving me conflicting answers on wire size for a long run. The run is almost 400 feet(up and down included) from the main panel to the sub panel. 100 amps 120/208 3 phase. Using copper THHN and 3% VD, what size wire?
While we're at it, how much would you bid? Most of the run is 25ft in the air and you need to add 3 30 amp 3 phase outlets to plug in equipment near the new sub. The panels are seimens bolt in and the conduit needs to bew EMT, you provde the lift. Thanks!

Work Gear for Electricians and the Trades
Re: Quick wire size question. #12898
08/20/02 10:58 PM
08/20/02 10:58 PM
J
jo  Offline
Member
Joined: Apr 2002
Posts: 21
Oakland, California
10,700 #2 wire 2"emt

Re: Quick wire size question. #12899
08/21/02 05:00 AM
08/21/02 05:00 AM
S
scjohn  Offline
Member
Joined: Jul 2002
Posts: 74
charleston, SC, USA
With a full load and 3.1% you need to run a 2/0. 3/0 gets you douwn to a 2.5% v/d..
To early in the morning to help with the quote..
SC John.

Re: Quick wire size question. #12900
08/21/02 07:27 AM
08/21/02 07:27 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Ditto SCJohn,
2.55% VD with 3/0
2" EMT

Re: Quick wire size question. #12901
08/21/02 09:15 AM
08/21/02 09:15 AM
J
jo  Offline
Member
Joined: Apr 2002
Posts: 21
Oakland, California
Sorry
3/0 is correct

Re: Quick wire size question. #12902
08/21/02 09:38 AM
08/21/02 09:38 AM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
Feedback please - these VD calculations to determine the need for 3/0 conductor is based on a 100A draw - in truth this panel will not be pulling 100A...prob. won't even be pulling 90A....if you use 90A in your calculation your conductor size drops to 2/0. Not only does this lower the matl. cost it sure makes pulling into that 2" conduit a lot easier. My opinion is this: if you're going to be pulling more than 80A from a 100A panel, you should be upsizing it to begin with.

Re: Quick wire size question. #12903
08/21/02 09:53 AM
08/21/02 09:53 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Your calculation is based on Article 220. That is where your amps for your VD calc should come from.

Re: Quick wire size question. #12904
08/21/02 08:36 PM
08/21/02 08:36 PM
E
Electric Eagle  Offline OP
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
Thanks to everyone! My ElectriCalc was telling me 3/0 CU, but I didn't want to believe it. I mean 4/0 AL is good for 200. The actual run is more like 370ft and I can live with just over 3%VD, so I did the quote with 2/0, although my gut tells me that they will never pull more than 50 or 60 amps in which case #1CU would be fine. I gave the bid the way I would want it, if I lose it to someone using #1 or #2, then so be it. Thanks Guys

Re: Quick wire size question. #12905
08/21/02 09:02 PM
08/21/02 09:02 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
George is right. Use 220, not your gut feeling (I thought you said 100 amp load). [Linked Image]

Re: Quick wire size question. #12906
08/21/02 09:26 PM
08/21/02 09:26 PM
E
Electric Eagle  Offline OP
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
electure, I ignored my gut feeling and went with the max, but I doubt my competion did, that's what I was saying. Acutally when you add the 3 pieces of equipment, the total max amps is 58 (22,22&14) and will all run at the same time. But this is for a 100 amp sub panel and someone in the future could add more equipment or even another sub panel off of this one. Therefore I wanted to make sure the wire could handle max load without substanial VD.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,601 Are you busy
180,416 Re: Forum
170,871 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 14 (0.010s) Memory: 1.0075 MB (Peak: 1.1820 MB) Zlib enabled. Server Time: 2018-01-23 19:56:11 UTC