Selecting AIC #128908
03/23/04 07:03 PM
03/23/04 07:03 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
The customer wants a 480v, 125a MLO Sq. D NF panelboard for the service on an agricultural building. The PoCo transformers are pole mounted, delta-delta. Let's assume we have three 50kva transformers.

How do I select the correct aic breaker? The available sizes are;
65,000 aic
35,000 aic
18,000 aic

thanks,
GJ

[This message has been edited by golf junkie (edited 03-23-2004).]

Tools for Electricians:
Re: Selecting AIC #128909
03/23/04 07:30 PM
03/23/04 07:30 PM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Take a look at http://www.ecmweb.com/ar/electric_basic_shortcircuit_current/
for an extremely basic introduction to short circuit calculations. Find out the transformer impedance, and presume every other impedance in the short is zero, to get a conservative approximate value.

-Jon

Re: Selecting AIC #128910
03/23/04 08:19 PM
03/23/04 08:19 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
thanks jon, that was helpful

Re: Selecting AIC #128911
03/23/04 08:43 PM
03/23/04 08:43 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
The utility should be able to provide that information for the service entrance location. Needed transfomer impedance data to estimate that value is not generally available to the electrician working downstream of the meter.

Also, that relieves the electrician of having to do short-circuit estimates for service-entrance equipment.

Re: Selecting AIC #128912
03/23/04 09:02 PM
03/23/04 09:02 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Determine the full load current on the secondary, divide that number by the percent impedance of the transformer, and that gives you a conservative value at the secondary stabs of the xfmr. Depending on the length of the secondary conductors, that will further reduce the available fault current.
For example, 150000/480/1.73/.02=9030A of fault current at the secondary stabs.
You would be safe choosing the lowest AIC of the group.


Ron
Re: Selecting AIC #128913
03/24/04 09:34 AM
03/24/04 09:34 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Warning - the Square D NF panelboard is not rated for use on 480V delta systems. The NF panel has a slash rating of 480Y/277, so it can not be used on circuits with more than 277V to ground. You need to switch to their I-Line panel instead.

Re: Selecting AIC #128914
03/28/04 08:45 AM
03/28/04 08:45 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Ron
That is good info that 'us' electricians can actually use.
JBD
That is very observant and a key pickup.
Thanks

Pierre


Pierre Belarge

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,827 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9825 MB (Peak: 1.1378 MB) Zlib enabled. Server Time: 2018-01-18 11:48:36 UTC