Light Switches and Meter Readings #128876
03/08/04 09:06 PM
03/08/04 09:06 PM
T
ThinkGood  Offline OP
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
If a meter is placed in line with the two wires that make up the switched part of a lighting circuit, without the switch, should there be a reading of 120VAC?

To clarify, the "hot" is what would be switched (hopefully...) There is the conductor going to the top screw of the switch, and a conductor going to the bottom screw. Touch the two conductors together--by flipping the switch so to say--and the light goes on. What if a meter is placed between the two conductors, rather than a switch? Should there be any reading on the meter? Should the light go on?

Tools for Electricians:
Re: Light Switches and Meter Readings #128877
03/08/04 09:42 PM
03/08/04 09:42 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Thinkgood;

If you place the leads of a Volt Meter across the Terminals of a 1 Pole 1 Throw switch, which has either a Ballast or Incandescent Lamp on the Load side (which is not Barbequed / Failed Open - actually works...), you will find:
<OL TYPE=A>

[*] With Switch Closed - Zero Volts,

[*] With Switch Open - 120 Volts.
</OL>
FYI: above examples assume the system is 120 VAC, and the Switch Contacts are not pitted to death (make very good contact with less than 1 volt loss across the Switch).

So to answer your Q in full, if the Switch is removed and the Test Leads of a Volt Meter applied in its place, there will be a Voltage reading.
The Lamp will not light up, due to the Volt Meter's Impedance limiting the Current in this Series Circuit.
FYI: The Lamp and Meter will be in series, so it is now a series circuit. Highest Voltage will be measured across the highest Resistance / Impedance.

Hope this is what you are looking for!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Light Switches and Meter Readings #128878
03/08/04 09:50 PM
03/08/04 09:50 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
TG, that is a fundamental but important question. With the ususal high-impedance digital multimeter set to and jacked into a 200V-up AC-volt range, expect a reading of 120V with NO lighted lamp. But, if you set to and jack into an 2-amp & up AC-current scale, the meter should read the lamp load current {100 watts = ~0.8 amps} with a bright lamp.

The wiring position on plain-vanilla toggle-switch terminals usually does not matter.




[This message has been edited by Bjarney (edited 03-08-2004).]

Re: Light Switches and Meter Readings #128879
03/09/04 08:14 AM
03/09/04 08:14 AM
T
ThinkGood  Offline OP
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
That's what I was looking for. Thank you, gentlemen.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,392 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9591 MB (Peak: 1.0895 MB) Zlib enabled. Server Time: 2018-01-22 16:30:47 UTC