#128847 - 02/22/04 11:59 AM Is there something wrong with my calculation?  
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Hi,

I've been scratching my head over something. I have a scenario (theoretical) where you can either use 2 wires @ 230V or 3 wires @ 200V 3-ph. The size of the wires is limited by voltage drop, which is the same percentage wise for both cases. According to textbooks and common knowledge, 3-phase is more efficient than just using two wires. But I fail to arrive at this result in this case.

If I put 1A load the 3-ph case I need 1.73/1.15 = 1.5A single phase to get the same power. This means I have to increase the cross sectional area of the conductors by 50% compared to the 3-phase case. But I only need 2 wires instead of 3 and am back at the same amount of copper.

Is there something wrong with my calculations? Wouldn't be the first time... [Linked Image]


Tools for Electricians:

#128848 - 02/22/04 03:55 PM Re: Is there something wrong with my calculation?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
C-H, that is a great riddle/brainteaser. The “trick” is 3ø versus 1ø power must be compared at the same voltage.

1.5 amperes at 230V 1ø is 345VA, where
1 ampere at 200V 3ø is 346.4VA, BUT
1 ampere at 230V 3ø is 398.4VA.
Ratioing, 345/398.4 yields 0.866, exactly as expected.

Does that help?


#128849 - 02/23/04 08:47 AM Re: Is there something wrong with my calculation?  
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Thanks! I needed to check my calculation with someone. I wanted the same potential to ground for both cases (wye or center tapped source).

By the way, are you and Busbar one and the same person?


#128850 - 02/23/04 11:16 AM Re: Is there something wrong with my calculation?  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
C-H,

You've found an identity [Linked Image] (In the mathematical sense.) For the same potential to neutral and the same 'aggregate current', you get the same VA delivered to the load, no matter 1 phase or 3 phase or 17 phases [Linked Image]

-Jon


#128851 - 02/23/04 11:25 AM Re: Is there something wrong with my calculation?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
C-H — Yes, but only on alternate Tuesdays. ;-)



Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7688 MB (Peak: 0.9093 MB) Zlib enabled. Server Time: 2017-07-27 02:42:55 UTC