#128377 - 02/07/03 12:06 PM Ground Resistance ?  
VOLTS  Offline
Member
Joined: Jun 2001
Posts: 21
I have to install a static ground indicator for a railcar solvent unloading station. The indicator has an intrinsically safe circuit in it. I have read that I.S circuits need very low ground resistance to work properly. I have heard of a product that is put around the ground rod or grounding system to help lower the resistance to ground. Also has anyone used the clamp on resistance testers from AEMC? I am resposible for the grounding system of a large chemical plant were grounding is VERY important. Would this instrument be wise investment or are there other testers that would be a better choice?


Tools for Electricians:

#128378 - 02/08/03 09:13 PM Re: Ground Resistance ?  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Bjarney is really sharp as to Grounding System testers and Chemical additives for fixing R / Z levels.

Simply the goal is to have everything in the "immediate Area" at the same potential - so there will be a very low chance to build up an Electrostatic charge between the car(s) and the pumping apparatus.

Impedance and / or Resistance of the Electrode system may not be a high criteria, whereas an Equipotential Plane may be more important.

Got any Specs???

Scott35 S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#128379 - 02/09/03 02:10 AM Re: Ground Resistance ?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
<GASP! Who? Me?> OK, one needs to understand several aspects of grounding, particularly where hazardous locations are concerned. Intrinsically-safe circuits do not necessarily require a low grounding-electrode resistance, but that would be an engineering call by the indicator producer and covered in installation instructions—which should be carefully understood and followed. The more important considerations are {ground} continuity of all conductive surfaces in the area where the work takes place, to keep potential difference as low as reasonably achievable.

As far as testers, you may want to contact AEMC or Megger sales reps and ask them to demo “fall-of-potential” or “three-point” and clamp-on test sets. They all have their positive characteristics, as well as limitations.

The fill material I’m familiar with is
“Lynconite” http://www.lyncole.com/html/Misc.asp#salt
“GEM” http://www.erico.com/erico_public/product/GEM.asp

That’s the short version. Don’t hesitate to follow up with any other questions.


#128380 - 02/20/03 11:47 PM Re: Ground Resistance ?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Are you referring to field installing intrinsically safe wiring with barriers and/or isolators? Or are you simply using a piece of equipment that is intrinsically safe?
If you are installing your own IS circuitry, tell me what brand of barriers or isolators you are using, and I may be able to offer some help.
As Bjarney said, the low impedance grounding doesn't refer to earth resistance, but a ground path sufficiently low to allow the barrier to operate should a fault occur in the hazardous location. The design of the barrier will dictate how this is accomplished.

[This message has been edited by Redsy (edited 02-20-2003).]



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.045s Queries: 14 (0.035s) Memory: 0.7615 MB (Peak: 0.8912 MB) Zlib enabled. Server Time: 2017-10-22 10:11:33 UTC