Strange ....Please read #128186
09/16/02 12:52 AM
09/16/02 12:52 AM
S
Sean WB  Offline OP
Member
Joined: Sep 2002
Posts: 111
South TX
scenario: A barn is fed from the house main panel with 60 amp dp breaker. There is a Sub in the barn. homeowner said breaker in barn was tripping for air compressor. They had their son check it, he tried to wire the 240v motor from from one leg. After smelling horse s$#t for an hour I finally found he wired it from one leg in panel.
Compressor was wired correctly, everything ran fine, no trips. I watched it for a while on amp probe. I was there most of the day installing fans etc etc. compresor worked fine.
I get called back a week later, compressor was not running. I checked voltage at main, 240 across, 120 to ground. I checked at sub panel , I had 240 to ground and 0 on other leg, 175 across??
I pulled all breakers from panel and checked:everything was fine:120 to ground, 240 across. When I replace the breakers one by one untill i get to the lighting circuit (by the way its a new panel, new breakers)I get 175 on one leg and like 30 on the other. Everything in the barn reads like this. it is still reading normal at the main when it does this. what is going on?? I have isolated all circuits and metered them for shorts, everything looks fine.
I am going back in the morning to change out the 40 year old ceramic light fixtures.
any pointers would be greatly appreciated.
I will check in the morning before I go to the site,


I did not get as think so badly as you shocked I did.
Tools for Electricians:
Re: Strange ....Please read #128187
09/16/02 12:57 AM
09/16/02 12:57 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Sound like an open neutral, or a neutral with a corroded connection (or loose) that would cause a large impedance.

How good of condition is the sub-panel in?

Signs of corrosion? Anti-oxidant used?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Strange ....Please read #128188
09/16/02 01:19 AM
09/16/02 01:19 AM
S
Sean WB  Offline OP
Member
Joined: Sep 2002
Posts: 111
South TX
the panel is new sqareD qp line. at which connection are you talking about? I added a ground rod at barn since the span for the service to the barn was about 150' and I thought the ground size was too small and yes possibly aged since it is 30 years old and is a stranded bare #8. I am in a rural area of south TX where heat and humidity do a number on everything, even me :O)

[This message has been edited by Sean WB (edited 09-16-2002).]


I did not get as think so badly as you shocked I did.
Re: Strange ....Please read #128189
09/16/02 05:18 AM
09/16/02 05:18 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
Quote
175 on one leg and like 30 on the other

2nd 66's response there......

Sean,
i think 66's had a lot of experience with an article 547, agricultural buildings, which details the finer points here..... [Linked Image]

Re: Strange ....Please read #128190
09/16/02 03:49 PM
09/16/02 03:49 PM
S
Sean WB  Offline OP
Member
Joined: Sep 2002
Posts: 111
South TX
turns out they (UT CO)kernied the neutral at service drop for the barn.there are three weather heads on the pole and it looks like a birds nest up there.I continued to have same problems today, so I am going to run a new underground service tomorrow for the barn and discontinue the overhead service.
Its either an insulation breakdown in the ungrounded conductors feeding the barn (which are 30+ years old) or I have lost a neutral at the bird nest.
Either way, this was definitely a learning experience.
I need to invest in a megger, whats a good name to get ??


I did not get as think so badly as you shocked I did.
Re: Strange ....Please read #128191
09/16/02 04:07 PM
09/16/02 04:07 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Lots of Extech meters here...
https://www.electrical-contractor.net/The_Store/EX/GRT_Main.htm

Can't go wrong with Fluke either...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Strange ....Please read #128192
09/16/02 05:18 PM
09/16/02 05:18 PM
S
Sean WB  Offline OP
Member
Joined: Sep 2002
Posts: 111
South TX
which megohm meter should i look for? I just do mostly residential, light commercial . these exteck say they are for anaolog and communication cables.I would just like to get hold of a plain ol simpson crank type megger, you know? no fancy digital malarky


I did not get as think so badly as you shocked I did.
Re: Strange ....Please read #128193
09/16/02 08:04 PM
09/16/02 08:04 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Woops! My bad!

Telcom indeed...

Can't seem to find any crank type for less than $600!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Strange ....Please read #128194
09/17/02 12:53 PM
09/17/02 12:53 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Buy a unit with both 1 AND .5kV ranges. It would be money well spent on a tester with built-in 600VAC measurement, to be damn sure the circuit’s deenergized before trying to meg. [Escaping smoke is expensive.]

Biddle/AVO's "A Stitch in Time" booklet is excellent reading. Also stuff at: http://www.avointl.com/us/publications/Index.asp




[This message has been edited by Bjarney (edited 09-17-2002).]

Re: Strange ....Please read #128195
09/17/02 06:01 PM
09/17/02 06:01 PM
S
Sean WB  Offline OP
Member
Joined: Sep 2002
Posts: 111
South TX
I ran a new underground service this morning to the barn. Evrything lined out great (Thank GOD)

Man , there was 50 volts to ground on the sub panel in that barn!!
I had to use a suicide receptacle from that S-P to run my hole saw for the new service, It was very nerve racking. Thanks for all the pointers, I think I like it here:O)

[This message has been edited by Sean WB (edited 09-17-2002).]


I did not get as think so badly as you shocked I did.
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,231
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,601 Are you busy
180,412 Re: Forum
170,870 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 1.0246 MB (Peak: 1.1999 MB) Zlib enabled. Server Time: 2018-01-23 17:40:37 UTC