Strip Mall House Panel #120812
05/06/05 02:17 PM
05/06/05 02:17 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,481
NY, USA
Quote
This was a house panel on the back side of a strip mall. I was called out to trouble shoot and repair parking lot lights that were not working. After researching, I found the panel. First the total enclosure had been hit numerous times by trucks. I could barely access it with out pulling it from the wall. The problem, it turns out, was a loose main lug which eventually destroyed the conductor. But, as I looked at all the controls, nothing was right...

The conductors coming from the meter terminated at a 150 amp main breaker. (Barely held on by short screws) >From there the went to a old contactor which was operated by a time clock. The time clock in turn was powered by the load side of the main.(no inline fuse) back to the feeders. From the contactor they terminated to a federal pacific main lug panel. So the whole panel was being shut down during the day. The last 2 pics is what I did to repair it...

- John Cole
[Linked Image]

[Linked Image]

[Linked Image]

Tools for Electricians:
Re: Strip Mall House Panel #120813
05/07/05 05:12 AM
05/07/05 05:12 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Nice looking rework. [Linked Image]

I do have a question, other than the unfused time clock feed whats wrong with shutting the whole panel down by time clock?

Contactor controlled panels are common for lighting circuits.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Strip Mall House Panel #120814
05/08/05 05:08 AM
05/08/05 05:08 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I do not want to seem critical here however do I see all the branch neutrals leaving the panel near the top and all the branch hots leaving from the bottom?

This can / will cause the metal enclosure of the panel itself to get warm or hot depending on the load carried by those conductors.

It is also a violation of 300.3(B).


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Strip Mall House Panel #120815
05/09/05 09:20 AM
05/09/05 09:20 AM
M
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
Unless the case is non-ferrous.


Mike Wescoatt
Re: Strip Mall House Panel #120816
05/09/05 12:50 PM
05/09/05 12:50 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
iwire posted:

Quote
I do have a question, other than the unfused time clock feed whats wrong with shutting the whole panel down by time clock?


After wondering the same thing and looking at the new installation, my guess would be that the individual contactors on each group of parking circuits would tend to last longer, as the stress of load make/break is distributed instead of concentrated on one contactor.

Also, failure of any one contactor would not leave the entire lot in the dark.

Good call on the hot/neutral separation.


Stupid should be painful.
Re: Strip Mall House Panel #120817
05/10/05 07:35 PM
05/10/05 07:35 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
This isn't a violation of300.3(B)

........contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord.......

I don't see this as being any of the above.
This is in an enclosure.

It is a violation of 300.20, though. "Induced Currents in Metal Enclosures or Metal Raceways"

Re: Strip Mall House Panel #120818
05/14/05 05:25 AM
05/14/05 05:25 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
electure

Quote
It is a violation of 300.20, though. "Induced Currents in Metal Enclosures or Metal Raceways"


Good point, I gave the wrong reference. [Linked Image]

Bob



[This message has been edited by iwire (edited 05-14-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,558 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9857 MB (Peak: 1.1397 MB) Zlib enabled. Server Time: 2018-01-20 03:22:53 UTC