#11921 - 07/26/02 08:48 PM how many circurts per neutral  
lynnbar  Offline
Junior Member
Joined: Jul 2002
Posts: 6
volga west virgina usa
just a dumb little question, ive seen this in a few boxs where they will use one neutral per three circurts, I myself like to give each circurt its own neutral.
is this becoming or has been a way to save money. just wondering is all thanks joe


Work Gear for Electricians and the Trades

#11922 - 07/26/02 09:19 PM Re: how many circurts per neutral  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Joe, I'm going to assume you are new into the trade. Please research branch circuit multiwire covered in the NEC Article 100.
as well as 300 and 310 and more.

I don't mean to leave you hanging, but if you read these articles it will help more than an answer on the internet.

Remember that a grounded conductor per one circuit is not a neutral in reality.

Roger


#11923 - 07/26/02 09:27 PM Re: how many circurts per neutral  
lynnbar  Offline
Junior Member
Joined: Jul 2002
Posts: 6
volga west virgina usa
roger,
thanks and youre not leaving me hanging there at all. ill take the time to check it out. Joe


#11924 - 07/26/02 10:05 PM Re: how many circurts per neutral  
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
Joe -

You asked if 'this' was a way of saving money....I'm sure that may play some part with this practice, but if you check out 310-15(b)(4)(a) [1999] this will give a good reason for using the shared neutral. Example: if you tried to pull 6 circuits in a conduit using your one-neutral-per-circuit method you would have to derate the conductors 50% (Table 310-15b2a)... #12 THHN would only be rated for a 15A circuit ... using the shared neutral process you only derate 20%....in fact, you could get nine 20A circuits (using #12THHN) in one conduit (shared neutral method)vs. only 4 circuits using your method....god I hope I didn't blow my arithmetic!


#11925 - 07/26/02 10:10 PM Re: how many circurts per neutral  
lynnbar  Offline
Junior Member
Joined: Jul 2002
Posts: 6
volga west virgina usa
Dana,
that clears it up for me and i do see your point. Joe


#11926 - 07/26/02 10:20 PM Re: how many circurts per neutral  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
lynnbar,

You have to realize that this is only an option under certain circumstances, it cannot always be done. For what you describe it would have to be a Three-Phase system and all on different 'phases' or 'legs'.

Bill


#11927 - 07/26/02 10:24 PM Re: how many circurts per neutral  
lynnbar  Offline
Junior Member
Joined: Jul 2002
Posts: 6
volga west virgina usa
bill,
thats where i seen this at on a 3 phase panel, joe



Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7835 MB (Peak: 0.9347 MB) Zlib enabled. Server Time: 2017-07-24 22:45:23 UTC