ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,333 Are you busy
174,803 Re: Forum
167,182 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#118891 - 11/05/04 11:23 PM This Old House  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,447
NY, USA
Quote
This is a project that started out as a replace-the-1940s-outlets, and turned into a partial rewire.

The first two shots are in the attic...a violation of Article 300.11 Securing and Supporting. Notice the homemade cover in the second shot.
[Linked Image]

[Linked Image]
Quote
The next three shots are of a breezeway outlet. The first picture is to show that it looks like a correctly polarized outlet. The second shot is with the receptacle removed...no connector, and notice the color coding...Red to neutral, Black to ground, and White to power. You would have thought by chance he would have had one of them right. The third shot shows I had plenty of slack to work with on this one...not so lucky on a few of the others in the house.
[Linked Image]

[Linked Image]

[Linked Image]


Tools for Electricians:

#118892 - 11/05/04 11:27 PM Re: This Old House  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,447
NY, USA
Quote
The next shot is of a PC closet light. This is exactly how it was...pulling down a little further every time she yanked on it. I call this one "The Firestarter".
[Linked Image]
Quote
The next shot is a laundry/freezer receptacle that was split-wired for the two 20-amp dedicated circuits. The breakers weren't handle-tied, and the outlet isn't 20-amp, violations of Articles 210.7(C) and 210.21(B)(1).
[Linked Image]
Quote
The last three shots are of the living room receptacle. The first one shows that it was fed by UF NM wiring with no connectors. This may be some original post-WWII NM circa 1945. The second shot shows a behind-the-wall shot with the outlet removed. The last shot shows how this receptacle was fed from a plug. It was plugged in prior to this shot being taken. Another outlet in the attic was fed from this mess.

Dave55
[Linked Image]

[Linked Image]

[Linked Image]


#118893 - 11/06/04 12:10 AM Re: This Old House  
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
My....GOD!

How did they manage to connect what I assume is 14 AWG solid wire to a plug that is designed for maximum 16 AWG stranded wire???

I mean...those plugs are used for small things like lamps and TV sets and small-to-medium duty use appliances; certainly NOT for this!

I'm thinking that trying to bend those wires around the terminal screws would have probably cracked the rubber housing of the plug. [Linked Image]

Oh...and if anyone wonders what the wall plate to the right of the outlet is in Shot #5, It looks like a connection for a TV antenna -- 300-ohm twinlead type.

At least that's what I've seen them labelled in places like Radio Shack - back when they still sold that stuff.

Talk about a PROJECT!


#118894 - 11/06/04 01:27 PM Re: This Old House  
sparked  Offline
Member
Joined: Sep 2003
Posts: 114
Raleigh
In Picture #2 you can see the great lengths peole will go to to save 70ยข or so...

I notice there are several of those outlets marked TV.. I guess this house was "wired for tv"?


#118895 - 11/06/04 03:52 PM Re: This Old House  
classicsat  Offline
Member
Joined: Nov 2002
Posts: 456
IMO that NM is too new to the that old. I'm guessing Later 1960/1970s there.
AFAIK, pre 1960 NM was the tar/paper /cloth stuff (with some sort of plastic or rubber insulated wires).



Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.004s) Memory: 0.7716 MB (Peak: 0.9068 MB) Zlib enabled. Server Time: 2017-07-26 00:50:02 UTC