ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Correct rotation, wrong sequence
by Potseal. 05/25/17 11:34 PM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
210.70 / Wall Switch / When adopted?
by gfretwell. 05/24/17 09:18 PM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,829 Are you busy
171,846 Re: Forum
164,750 Need opinion
Who's Online Now
0 registered members (), 59 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#118293 - 09/02/04 04:59 AM Should A Breaker Be 768 F?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
This is a Thermal Image of a Siemens bolt on panel from Capt. Al. The screw holding a single pole 20 amp breaker to the bus was loose.

[Linked Image]

The 409 C number is the temperature at the cross hairs.

Now this panel needs replacment, the copper bus for phase "B" is now gray.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Tools for Electricians:

#118294 - 09/02/04 08:45 AM Re: Should A Breaker Be 768 F?  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
What seems amazing to me is the tiny area that appears to be so hot. Although you can see the heat on the BØ, it looks like the heat dissipates pretty well, considering the extreme temp.


#118295 - 09/02/04 08:41 PM Re: Should A Breaker Be 768 F?  
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
This was taken in a computer testing lab with plenty of Liebert A/C cooling the area. Probably helped the heat to dissipate. The lighter the blue color on "B" phase is the heat dissipating over the bus. Darker blue is a cooler temp.

The circuit fed a dedicated receptacle for computer equipment. The only problem was someone plugged six five foot plug strips into the dedicated circuit. "IT" guys just plug and play.


#118296 - 09/03/04 09:20 PM Re: Should A Breaker Be 768 F?  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
Or should it be "plug and pray?"


#118297 - 09/05/04 04:07 PM Re: Should A Breaker Be 768 F?  
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Doug, you are right. With "IT" guys it should be plug and pray. The above pic tells it all.



Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.7673 MB (Peak: 0.9084 MB) Zlib enabled. Server Time: 2017-05-26 20:51:01 UTC